Have you confirmed what the temps are expected to be below the unit heater?  
The manufacturer’s data (or the mech engineer) may be able to provide this info.

Cheers
Don


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Silva
Sent: 2018/05/02 11:23 AM
To: [email protected]
Subject: Re: ESFR sprinklers near unit heaters

Even if in the 7 foot unit heater zone, with the possibility of a sprinkler 
being activated? Would it be a lesser evil if a non-ESFR 286 deg.F sprinklers 
having the same k factor as the ESFR sprinklers are used only near the unit 
heaters with the rest of the system being ESFR?
Tony

On Wed, May 2, 2018 at 8:59 AM, Mike Hairfield 
<[email protected]<mailto:[email protected]>> wrote:

Use the 212 deg. ones.



ASCOA used to make a 286 deg. one but they are out of business.



Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Tony Silva <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 2, 2018 10:57 AM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR sprinklers near unit heaters

Are there any ESFR sprinklers rated for 286 deg.F? If not, how would you locate 
them near unit heaters when it is next to impossible to maintain a minimum 7 
feet clearance? How have others solved this problem?
Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to