All warehouses (at least all that I have seen), have unit heaters and
installed as high as possible to maximize storage height. Unless the unit
heaters are maximum 2 feet wide, they are generally obstructions to the
roof ESFR sprinklers requiring additional sprinklers below the bottom level
of the unit heaters. Can't the sprinklers below the bottom level of unit
heaters be considered similar to those below overhead doors? If not, then
ESFR sprinklers cannot be installed in any warehouse with unit heaters, if
the NFPA requirements for sprinklers near heat sources also has to be
followed.

I like Mike, Don and Bruce's solutions of using 212 deg.F ESFR sprinklers
below the unit heaters, if the greater evil is using 286 deg.F non-ESFR
sprinklers at this location.

Tony

On Wed, May 2, 2018 at 12:38 PM, Roland Huggins <[email protected]>
wrote:

> Other than explicitly stated allowances (such as under overhead doors),
> you can not mix sprinkler types.  The really bad news is, if you can not
> meet all the requirements, that eliminates that type of sprinkler as an
> option.
>
> Roland
>
> Roland Huggins, PE - Senior VP Engineering
>
> American Fire Sprinkler Assn.
>
> Dallas, TX
>
> http://www.firesprinkler.org
>
>
> Fire Sprinklers Saves Lives
>
>
>
>
> On May 2, 2018, at 8:22 AM, Tony Silva <[email protected]> wrote:
>
> Even if in the 7 foot unit heater zone, with the possibility of a
> sprinkler being activated? Would it be a lesser evil if a non-ESFR 286
> deg.F sprinklers having the same k factor as the ESFR sprinklers are used
> only near the unit heaters with the rest of the system being ESFR?
>
> Tony
>
> On Wed, May 2, 2018 at 8:59 AM, Mike Hairfield <[email protected]> wrote:
>
>> Use the 212 deg. ones.
>>
>> ASCOA used to make a 286 deg. one but they are out of business.
>>
>> Mike
>>
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to