You could refer him to 2016 NFPA 13

9.2.3.5.2.2 Unless flexible sprinkler hose fittings in accordance with 
9.2.1.3.3.1 are used, the hanger closest to the sprinkler shall be of a type 
that prevents upward movement of the pipe.

Then show him that you are in compliance with 9.2.1.3.3, and explain that the 
reason the hanger closest to the sprinkler does not have to prevent upward 
movement, is specifically because the bracket that is provide with the listed 
flex drop assembly does the job of preventing the upward movement.

If you want to make him not feel so bad, you could say something about how he 
is correct in thinking this would be an issue, if not for the bracket attached 
to the ceiling.

Maybe show him how they attach. He would have to be pretty dumb to see one 
installed correctly and still think this would be an issue.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Wednesday, May 30, 2018 8:59 AM
To: [email protected]
Subject: [EXTERNAL] Ceiling Grids and Flex Drops

I have a AHJ that is questioning the use of Flex Drops especially the Victaulic 
ones. He says that they are so flexible that when a sprinkler goes off the jet 
effect is going to lift the sprinkler up through the ceiling. I told him that 
the drops are mechanically attached to the ceiling grid and in order to lift up 
they would have to lift the entire weight of the ceiling grid, ceiling tiles, 
the lights and HVAC diffusers. His answer prove, it either by letter from the 
manufacturer or from someone a lot higher up the food chain than either he or I 
am. Or something specific in NFPA 13 that says he is wrong.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
W: 877.324.ROWE  *  F: 570.837.6335
PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842
505 A Cornerstone Court * Hillsborough, NC 27278
RoweSprinkler.com  *  
[email protected]<mailto:[email protected]>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to