The "jet effect" were the AHJ's words, the man can barely read a set of 
calculations, I wasn't going to get into physics with him.



-----Original Message-----
From: bcasterline <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Thu, May 31, 2018 3:57 pm
Subject: Re: Ceiling Grids and Flex Drops

Newton's Third Law?After I fry this fresh cloud based sprinkler applet I'll 
check your  math Allan and respond off Forum if need be. :)You know I worked 
with the inventor of the Hose Monster? He told me  when where and how he got 
the idea.  I'm the Forest Gump of this industry:*worked with inventor of 
sprinkcad*worked with inventor of autosprink*worked (and still do) for the 
first person to print the first  density/area curves for TC consideration.You 
can see a pic of him here:https://www.fsc-icalc.comBradQuoting AKS-Gmail-IMAP 
<[email protected]>:> So what is this jet effect that is going to lift the 
sprinkler? The  > forces on this sprinkler are going to be the end pressure 
force and  > any momentum change force.>> Lets say this is a 5.6k sprinkler 
having a .438” diameter orifice.  > The orifice area is about 0.1507 square 
inches. That is about 1lb  > for 7 psi and about 12 lbs for 80 psi since those 
pressure numbers  > are gage pressure referenced from atmosphere pressure. The 
orifice  > end pressure force must be why we have the last sprinkler surge  > 
restraint rule where there is not much piping for counter balance.>> Now what 
is the momentum change? The water comes streaming out the  > nozzle and slams 
into the deflector that is connected to the nozzle.  > There is a canceling 
out. Then the water changes momentum to go  > radially. Lets say that is equal 
in all directions. So the radial   > momentum changes cancel each other. Think 
of a Hose Monster. The  > momentum change situation is not the same as that of 
hose nozzle  > stream needing some beef to hold it.>> It would not take much to 
demonstrate this. Take a flex drop and  > operate it with an open sprinkler and 
compare to operating it also  > with a busted off sprinkler that has no 
deflector and arms. Pick a  > nice hot day to do this.>>>> On May 30, 2018, at 
10:59 AM, Richard Mote  >> <[email protected]> wrote:>>>> I have a AHJ 
<> that is questioning the use of Flex Drops  >> especially the Victaulic ones. 
He says that they are so flexible  >> that when a sprinkler goes off the jet 
effect is going to lift the >> sprinkler up through the ceiling. I told him 
that the drops are  >> mechanically attached to the ceiling grid and in order 
to lift up  >> they would have to lift the entire weight of the ceiling grid,  
>> ceiling tiles, the lights and HVAC diffusers. His answer prove, it  >> 
either by letter from the manufacturer or from someone a lot higher  >> up the 
food chain than either he or I am. Or something specific in  >> NFPA <> 13 that 
says he is wrong.>>>> Richard Mote>> Design Manager>>>> W: 877.324.ROWE  ·  F: 
570.837.6335>> PO Box 407 · 7993 US Route 522, Suite 1 · Middleburg, PA 17842>> 
505 A Cornerstone Court · Hillsborough, NC 27278>> RoweSprinkler.com  ·  
[email protected]  >> 
<>_______________________________________________>> Sprinklerforum mailing 
list>> [email protected]>> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org_______________________________________________Sprinklerforum
 mailing 
[email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to