8ft is minimum distance between ESFR heads.

Note that the baffle option in other parts of Chapter 8 is not provided for 
ESFR's.  It's not so much of a skipping due to cold soldering issue but one of 
having too many heads open above the fire and starving the system of water.

I can almost hear Roland typing 'ESFR's are not always appropriate for your 
building (or something similar).

If you wanted to take the 'engineering' approach, one might make a case that 
this could be acceptable if one could prove that the calcs would work with the 
additional ESFR's flowing water.....thats one of those 'get it stamped and get 
a sign-off from the AHJ' scenarios.

Cheers
Don


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: 2018/05/30 11:14 AM
To: [email protected]; 
[email protected]
Subject: Re: ESFR closer than 8'

35' limited to 10'

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Mike Stossel <[email protected]>
Sent: Wednesday, May 30, 2018 9:12:40 AM
To: [email protected]
Subject: RE: ESFR closer than 8'

Is the building 30'0" high or lower?  If so would expanding your spacing to 
12'0" help?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum <[email protected]> On Behalf 
Of JD Gamble
Sent: Wednesday, May 30, 2018 11:07 AM
To: [email protected]
Subject: ESFR closer than 8'

I need some clarity on this one ....

Spacing ESFR 25.2K PNTs on 10 x 10 spacing in 30' bays @ 16" below ceiling.  
Line are equally spaced 5' from center of 36" deep beams.  I have an area where 
a full height wall is 11'-6" from a beam requiring an additional row of ESFR.  
When spacing the additional sprinklers at 8' between branch lines it places the 
additional sprinklers less than 8' from the adjacent line along the other side 
of the solid steel beam.  Is the beam sufficient (only 20" below the sprinkler) 
to prevent skipping?  Can I be less than minimum spacing (64sq.ft.) with the 
beam separating sprinklers?

Scratching my head here.....