Jerry, I understand what you're saying, and the theory behind it, but I don't think that is the correct interpretation of the code.
Per 2016 NFPA 13: 8.12.2.3 Minimum Protection Area of Coverage. The minimum allowable protection are of coverage (As) shall not be less than 64 ft2. The key is the definition of "protection are of coverage (As)". If you go back a page or two, you find this: 8.12.2.1 Determination of Protection Area of Coverage. The protection area of coverage per sprinkler (As) shall be determined in accordance with 8.5.2.1. Go back to that section, and you find... well I'm not going to type it all out, but the important part is that you use this formula: As = S x L And L is determined by "the larger of either twice the distance to the wall or obstruction or the distance to the next sprinkler. Assuming that the beam is considered an obstruction (head closer than 5 feet in this instance, see 8.12.5.1.1) then you are using the larger of either double the distance to the beam, or the distance to the next line. In this case, I'm guessing coverage area will end up being calculated at 80 square feet (8' x 10'), although I am guessing at the actual layout. Long story short: It is OK to be spaced less than 8 feet when there is an obstruction in the middle, in my interpretation. -Kyle M From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Costello Sent: Wednesday, May 30, 2018 8:12 AM To: [email protected] Subject: [EXTERNAL] RE: ESFR closer than 8' My understanding is that a beam or baffle does not work with ESFR sprinklers. This because the minimum square footage maintained by spacing requirements are figured into the 12 sprinkler heads used in the testing. Jerry Costello Lead design set Advance Fire Protection Since 1969 1451 W Lambert RD La Habra, Ca. 90631 714-526-2231- fax 562-691-5482 From: Sprinklerforum [mailto:[email protected]] On Behalf Of JD Gamble Sent: Wednesday, May 30, 2018 8:07 AM To: [email protected]<mailto:[email protected]> Subject: ESFR closer than 8' I need some clarity on this one .... Spacing ESFR 25.2K PNTs on 10 x 10 spacing in 30' bays @ 16" below ceiling. Line are equally spaced 5' from center of 36" deep beams. I have an area where a full height wall is 11'-6" from a beam requiring an additional row of ESFR. When spacing the additional sprinklers at 8' between branch lines it places the additional sprinklers less than 8' from the adjacent line along the other side of the solid steel beam. Is the beam sufficient (only 20" below the sprinkler) to prevent skipping? Can I be less than minimum spacing (64sq.ft.) with the beam separating sprinklers? Scratching my head here..... Life Safety Solutions of Sheridan JD Gamble [email protected]<mailto:[email protected]> (307) 763-3361
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org