Below from NFPA question site.
ESFR spacing
Question asked by NFPA FAQ<https://community.nfpa.org/people/nfpa_faq> on Apr 
6, 2018
Latest reply<https://community.nfpa.org/message/53498#comment-53499> on Apr 6, 
2018 by Janna Shapiro
·        Like<https://community.nfpa.org/message/53498> • Show 0 
Likes0<https://community.nfpa.org/message/53498>
·        Comment • 1<https://community.nfpa.org/message/53498#comments>
1. Can spacing between ESFR sprinklers be less than 8 ft if there is a beam 
between the sprinklers that would obstruct the discharge ? 2. Can the minimum 
protection area of ESFR sprinklers be less than 64 sq ft if there is a beam 
between sprinklers that would obstruct the discharge ?
I also have this question • 0<https://community.nfpa.org/message/53498>
Visibility:  NFPA 
Knowledgebase<https://community.nfpa.org/community/members-only/knowledgebase>6 
Views
Last modified on Apr 6, 2018 11:18 AM
Tags:fire protection 
systems<https://community.nfpa.org/community/members-only/knowledgebase/tags#/?tags=fire%20protection%20systems>
Content tagged with fire protection 
systems<https://community.nfpa.org/community/members-only/knowledgebase/tags#/?tags=fire%20protection%20systems>
nfpa 
13<https://community.nfpa.org/community/members-only/knowledgebase/tags#/?tags=nfpa%2013>
Content tagged with nfpa 
13<https://community.nfpa.org/community/members-only/knowledgebase/tags#/?tags=nfpa%2013>

Categories: NFPA 
13<https://community.nfpa.org/community/members-only/knowledgebase/content?filterID=contentstatus%5bpublished%5d~category%5bnfpa-13%5d>
·        1 Reply<https://community.nfpa.org/message/53498>
·        [Janna Shapiro] <https://community.nfpa.org/people/jshapiro>
Janna Shapiro<https://community.nfpa.org/people/jshapiro> [Employee] Apr 6, 
2018 11:18 AM<https://community.nfpa.org/message/53498#comment-53499>
Section 8.4.6.3 permits the use of ESFR sprinklers in buildings with 
unobstructed and noncombustible obstructed construction. One of the subsections 
to this 8.4.6.3.2 requires that in all cases the minimum sprinkler spacing and 
area of coverage comply with 8.12.2 and 8.12.3. Therefore, the minimum spacing 
and protection area cannot be reduced below the 8 ft and 64 square feet, 
respectively, if there are beams between the sprinklers that cause obstructions.
Like<https://community.nfpa.org/message/53498> • Show 0 
Likes0<https://community.nfpa.org/message/53498>
 Actions <https://community.nfpa.org/message/53498>


Jerry Costello Lead design set
Advance Fire Protection Since 1969
1451 W Lambert RD
La Habra, Ca. 90631
714-526-2231- fax 562-691-5482


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark.Phelps
Sent: Wednesday, May 30, 2018 9:47 AM
To: [email protected]
Subject: RE: [EXTERNAL] RE: ESFR closer than 8'

On the basis of this being the reason, how does one explain the recommendation 
from FMG to install ESFR sprinklers at 4’-0” on center in 2 directions below 
obstructions over 4 feet wide?
I’m not doubting the issue/concern, just trying to understand it better.

Mark at Aero
602 820-7894



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Wednesday, May 30, 2018 9:25 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: ESFR closer than 8'

My understanding is the same as Don stated.  It is not skipping or cold 
soldering.  It is too many sprinklers opening.  The baffle or curtain will do 
little, if anything, to alleviate that.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Fwww.mfpdesign.com-252F-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DHJ8OA4xyeHAoxXNz5mu-252FYfycgtd5nsFrrpvzulZiNkQ-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=n5OWiG2vIjL_9ydQKfjJ0DoiW_hUBubhixfX01PvgTU&s=PcD-RkwiMcCIXKvg41bnSVbd2dNzc8o0-RIIqlsdBPk&e=>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.facebook.com-252Fpages-252FMFP-2DDesign-2DLLC-252F92218417692-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DH-252BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=n5OWiG2vIjL_9ydQKfjJ0DoiW_hUBubhixfX01PvgTU&s=BSUU5ugxtlHH6jk_3HmzZsqR6cFxVSCbkK_SGgvRXRA&e=>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=n5OWiG2vIjL_9ydQKfjJ0DoiW_hUBubhixfX01PvgTU&s=eW_FxghRInhgq6nOevv0xAf341E5RwUn2HmQuOHbVFw&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=n5OWiG2vIjL_9ydQKfjJ0DoiW_hUBubhixfX01PvgTU&s=m26yd-hR2TOEIlsFhzIpZsLzSftOm2Au2S8pCwyuBIc&e=>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of JD Gamble
Sent: Wednesday, May 30, 2018 9:23 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: ESFR closer than 8'

Actually meant that for Kyle , … but feel free to inject Don 😊

Life Safety Solutions of Sheridan

JD Gamble
[email protected]<mailto:[email protected]>
(307) 763-3361

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of JD Gamble
Sent: Wednesday, May 30, 2018 10:22 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: ESFR closer than 8'

Don,

Understanding the concern about water droplets being elevated through and with 
the fire plume, does the beam still need some form of baffle or curtain to 
prevent cooling leading to skipping?  In your opinion….

Life Safety Solutions of Sheridan

JD Gamble
[email protected]<mailto:[email protected]>
(307) 763-3361

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Kyle.Montgomery
Sent: Wednesday, May 30, 2018 10:05 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: ESFR closer than 8'

Jerry,

I understand what you’re saying, and the theory behind it, but I don’t think 
that is the correct interpretation of the code.

Per 2016 NFPA 13:

8.12.2.3 Minimum Protection Area of Coverage. The minimum allowable protection 
are of coverage (As) shall not be less than 64 ft2.

The key is the definition of “protection are of coverage (As)”. If you go back 
a page or two, you find this:

8.12.2.1 Determination of Protection Area of Coverage. The protection area of 
coverage per sprinkler (As) shall be determined in accordance with 8.5.2.1.

Go back to that section, and you find… well I’m not going to type it all out, 
but the important part is that you use this formula:

As = S x L

And L is determined by “the larger of either twice the distance to the wall or 
obstruction or the distance to the next sprinkler.

Assuming that the beam is considered an obstruction (head closer than 5 feet in 
this instance, see 8.12.5.1.1) then you are using the larger of either double 
the distance to the beam, or the distance to the next line.

In this case, I’m guessing coverage area will end up being calculated at 80 
square feet (8’ x 10’), although I am guessing at the actual layout.

Long story short: It is OK to be spaced less than 8 feet when there is an 
obstruction in the middle, in my interpretation.

-Kyle M



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Costello
Sent: Wednesday, May 30, 2018 8:12 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: ESFR closer than 8'

My understanding is that a beam or baffle does not work with ESFR sprinklers. 
This because the minimum square footage maintained by spacing requirements are 
figured into the 12 sprinkler heads used in the testing.

Jerry Costello Lead design set
Advance Fire Protection Since 1969
1451 W Lambert RD
La Habra, Ca. 90631
714-526-2231- fax 562-691-5482


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: Wednesday, May 30, 2018 8:07 AM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR closer than 8'

I need some clarity on this one ….

Spacing ESFR 25.2K PNTs on 10 x 10 spacing in 30’ bays @ 16” below ceiling.  
Line are equally spaced 5’ from center of 36” deep beams.  I have an area where 
a full height wall is 11’-6” from a beam requiring an additional row of ESFR.  
When spacing the additional sprinklers at 8’ between branch lines it places the 
additional sprinklers less than 8’ from the adjacent line along the other side 
of the solid steel beam.  Is the beam sufficient (only 20” below the sprinkler) 
to prevent skipping?  Can I be less than minimum spacing (64sq.ft.) with the 
beam separating sprinklers?

Scratching my head here…..

Life Safety Solutions of Sheridan

JD Gamble
[email protected]<mailto:[email protected]>
(307) 763-3361

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to