Micah,

This sounds like a situation where using the "Localized Protection of
Exposed Combustible Construction or Exposed Combustibles" might be
appropriate.  8.15.1.5 (13 ed):

If the exposed combustibles are in the vertical partitions or walls around
all or a portion of the enclosure, a singlerow of sprinklers spaced not over
12 ft apart nor more than 6 ft from the inside of the partition

shall be permitted to protect the surface. The first and last sprinklers in
such a row shall not be over 5 ft from the ends of the partitions.

In this scenario you would only provide sprinklers along the exposed walls.
Based on what you have described, my opinion is that sprinklers are required
in at least a localized manner.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Micah Davis, SET
Sent: Friday, June 15, 2018 7:35 AM
To: SprinklerForum
Subject: Concealed Space

 

I have a project that has a concealed space with exposed wood wall framing.
I added concealed space sprinklers per 8.15.1.2.1.  The engineer is telling
me to remove them stating that, since the walls are not load bearing, they
are not structural walls.  He then references Appendix A for 8.15.1.2.1 that
states the requirements to protect the space does not apply for
"nonstructural" wood.  Has anyone seen this before?  What is the opinion of
the Forum?  

 

I will, of course, defer to the engineer, but I am recommending that the
contractor I'm working with get a letter from the engineer clearly stating
that they are requesting the sprinkler not be installed.

 

 


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV 

Dynamic Fire Designs


 


Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com <http://dynamicfiredesigns.com>  


Dynamic Fire Designs . 13063 County Line Rd., Box #87 . Spring Hill . FL .
34609

This message is confidential. It may also be privileged or otherwise
protected by work product immunity or other legal rules. If you have
received it by mistake, please let us know by e-mail reply and delete it
from your system; you may not copy this message or disclose its contents to
anyone. The integrity and security of this message cannot be guaranteed on
the Internet. 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to