If its a wall, it is structural.  It’s the presence of sufficient combustibles 
that drive the boat (such as a NONCOMBUSTIBLE space with big bundles of wiring)

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Jun 15, 2018, at 6:34 AM, Micah Davis, SET <[email protected]> wrote:
> 
> I have a project that has a concealed space with exposed wood wall framing.  
> I added concealed space sprinklers per 8.15.1.2.1.  The engineer is telling 
> me to remove them stating that, since the walls are not load bearing, they 
> are not structural walls.  He then references Appendix A for 8.15.1.2.1 that 
> states the requirements to protect the space does not apply for 
> "nonstructural" wood.  Has anyone seen this before?  What is the opinion of 
> the Forum?  
> 
> I will, of course, defer to the engineer, but I am recommending that the 
> contractor I'm working with get a letter from the engineer clearly stating 
> that they are requesting the sprinkler not be installed.
> 
> 
> Micah Davis, SET
> NICET #124745
> Water Based Systems Layout, Level IV  Dynamic Fire Designs
>  
> Mail: [email protected] 
> <mailto:[email protected]>
> Mobile: 931-242-1299
> www.dynamicfiredesigns.com <http://dynamicfiredesigns.com/> 
> Dynamic Fire Designs • 13063 County Line Rd., Box #87 • Spring Hill • FL • 
> 34609
> 
> This message is confidential. It may also be privileged or otherwise 
> protected by work product immunity or other legal rules. If you have received 
> it by mistake, please let us know by e-mail reply and delete it from your 
> system; you may not copy this message or disclose its contents to anyone. The 
> integrity and security of this message cannot be guaranteed on the Internet.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to