Ron must be feeling mellow. Sort of a mild rant. Caused by M’s being 20 games 
over 0.500?

Best.

Bruce 

> On Jun 16, 2018, at 09:25, Ron Greenman <[email protected]> wrote:
> 
> Where is the data that supports the need? I don't have the exact numbers in 
> my head this morning, nor am I willing to look them up but the statistics are 
> that somewhere above 90% of all fires are controlled by a single or two 
> sprinklers operating, and above 95% are controlled by three (anybody jump in 
> with the exact numbers), and since we design to nine or usually more 
> typically I'd say a safety factor is already built-in. I think if you look at 
> systems that have been overwhelmed you'll mostly find that maintenance was 
> not carried out properly, or TIs were not addressed, or fires got into 
> unsprinklered or under sprinklered attics, or any number of things that were 
> existing code deficient. I also think you'd find that many fires were 
> controlled by systems that were existing code deficient. My mind could be 
> changed if I were shown a significant amount of loss due to inadequate water 
> in the original design in buildings where there were no other factors as 
> stated above, but I'm not seeing a need. Additionally, in my neck of the 
> woods, all the metropolitan jurisdictions are already imposing a 10# or 10% 
> factor already. Most are holding to that number like it's gold and even if 
> the hose stream allowance takes you over the supply line by 1/2# you're 
> surely going to have to re-design. This is unreasonable already, and I 
> realize the FDs already often act like over-indulgent parents, so I'm 
> especially worried that if this 10#s is codified it will be an add-on to the 
> already existent 10#s. I see tanks and pumps in everyone's future because of 
> mistrust of municipal water systems. Rant over. Ron out.
> 
> 
> Ron Greenman
> 
> [email protected]
> 
> 253.576.9700
> 
> The Universe is monstrously indifferent to the presence of man. -Werner 
> Herzog, screenwriter, film director, author, actor and opera director (1942-)
> 
> 
>> On Sat, Jun 16, 2018 at 7:50 AM Scott Futrell <[email protected]> wrote:
>> As a plan specifier, plan reviewer and an investigator I see designs right 
>> to the supply and then as-built conditions far worse (read more demanding) 
>> than the design submitted with the calcs.  This is not a regional 
>> observation.
>> 
>>  
>> 
>> Additionally, I am aware of communities that lower elevated tank levels 20’ 
>> in winter to lower heating costs.  Contractors in those areas do NOT adjust 
>> flow tests for this seasonal variation.
>> 
>>  
>> 
>> No safety margin what-so-ever in NFPA 13 is unreasonable for a design 
>> standard.
>> 
>>  
>> 
>> Arguments on the floor including ‘requiring all systems to have back-up 
>> power’ were ridiculous.
>> 
>>  
>> 
>> Scott
>> 
>>  
>> 
>> Office: (763) 425-1001 x2
>> 
>> Cell: (612) 759-5556
>> 
>>  
>> 
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Steve Leyton
>> Sent: Friday, June 15, 2018 2:16 PM
>> To: [email protected]
>> Subject: RE: Safety Margin
>> 
>>  
>> 
>> That was the conversation on the floor of the code hearing.  The concerns 
>> underscored by the CAM were not about whether safety factor is a good 
>> practice, it was that a fixed minimum value as high as 10 PSI could trigger 
>> all sorts of cost-impact consequences, particularly in areas where pressures 
>> are middling to poor – in Rhode Island, 10 PSI could be 25-30% of the 
>> available pressure.
>> 
>>  
>> 
>> In the West, due primarily to the politics of drought, water districts are 
>> using models in lieu of physical flow tests.  Prudent and conservative 
>> programming makes it possible for them to issue safeguarded values from 
>> which it’s not necessary to reduce the available pressure.  For ex., City of 
>> San Diego uses a three-level safety factor in their (highly accurate) 
>> models:  starting with legacy drought water levels in the reservoirs, then 
>> factor the highest seasonal demand, then the highest peak day demand of that 
>> season.   The values we’re getting are usually significantly lower than what 
>> can be measured on the hydrant, and this practice isn’t without controversy 
>> because there are obvious complications that can and do occur, particularly 
>> with existing systems based on 20-year old (and older) pressures that were 
>> physically measured (with crappy equipment) when first designed and built.
>> 
>>  
>> 
>> But if modeling becomes the new normal, prudent water district engineering 
>> departments and fire departments they serve can coordinate manipulating data 
>> to include reasonable safety factors.  The range of variation in pressures, 
>> accuracy of flow test equipment, the use of modeling in many areas … there 
>> are too many variables to set a fixed minimum safety factor based on PSI, 
>> IMHO.
>> 
>>  
>> 
>> SML
>> 
>>  
>> 
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Parsley Consulting
>> Sent: Friday, June 15, 2018 12:00 PM
>> To: [email protected]
>> Subject: Re: Safety Margin
>> 
>>  
>> 
>> Richard,
>> 
>> If my memory is accurate of the issues raised in the discussion that 
>> ambiguity was a part of the differing viewpoints.
>> 
>> Some argued that 10 psi was not workable in their locale as their pressures 
>> were so limited that an imposition of 10 psi was simply to drastic and would 
>> result in much larger pipe sizes as a result.
>> 
>> Others argued that 10 psi was not enough, and in their area 10 psi didn't 
>> equal 10%, and there was some reluctance to base their designs on a pressure 
>> greater than 90% of the available.
>> 
>> It was quite a discussion. 
>> 
>> Ken Wagoner, SET
>> Parsley Consulting
>> 350 West 9th Avenue, Suite 206
>> Escondido, California 92025
>> Phone 760-745-6181
>> Visit the website
>> 
>> On 06/15/2018 10:23 AM, Richard Carr wrote:
>> 
>> Even though it is not in NFPA most AHJ’s require some sort of safety margin, 
>> 10%, 10 psi which we have had to provide for a long time so most designers 
>> know to leave safety margin in the calc’s. it would be nice if they all used 
>> the same amount.
>> 
>>  
>> 
>> Richard M. Carr, SET
>> 
>> Project Manager/Design
>> 
>> Diboco Fire Sprinklers, Inc.
>> 
>> 325 Jackson Loop Road
>> 
>> Flat Rock, NC  28731
>> 
>>  
>> 
>> [email protected]
>> 
>> 828-696-3400
>> 
>> 828-696-2288 Fax
>> 
>> 828-708-9118 Mobile
>> 
>>  
>> 
>> 
>> 
>>  
>> 
>> 
>> 
>>  
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Parsley Consulting
>> Sent: Friday, June 15, 2018 1:22 PM
>> To: [email protected]
>> Subject: Safety Margin
>> 
>>  
>> 
>> Scott,
>> 
>> Based on the material which was presented to the -24 and -291 committee 
>> meetings I believed the proposed safety margin and the means to calculate 
>> that margin there was some merit in the proposal. 
>> 
>> For reasons I don't quite remember the PI was voted down at the 2nd draft 
>> meeting.  I listened to some of the discussion, and there were some good 
>> points made.  I'm not terribly surprised it failed at the convention level.  
>> Perhaps the attendees were following the lead of the technical committees, 
>> and declining to overrule their decision.
>> 
>> sincerely,
>> 
>> Ken Wagoner, SET
>> Parsley Consulting
>> 350 West 9th Avenue, Suite 206
>> Escondido, California 92025
>> Phone 760-745-6181
>> Visit the website
>> 
>> On 06/15/2018 8:09 AM, Scott Futrell wrote:
>> 
>> Only that the 'safety margin' inclusion in the 2019 edition of NFPA 13 
>> failed, so it won't be included or required.
>>  
>> I consider this unfortunate, but I'd guess that not everyone on the forum 
>> would agree.
>>  
>> Scott
>>  
>> Office: (763) 425-1001 x2
>> Cell: (612) 759-5556
>>  
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of [email protected]
>> Sent: Thursday, June 14, 2018 5:46 PM
>> To: [email protected]
>> Subject: NFPA Vegas Convention
>>  
>> I didn't make it again this year.
>> "Caputo" is the only speaker name I recognized.
>> Anybody have any earthshaking epiphanies?
>>  
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>  
>>  
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to