We'll have to have that conversation over drinks one of these days.  As I 
understand it the NFIRS entries are often made by line fire fighters at the 
time of the fire, 0200 in the morning or what have you.  I was friendly with 
the former superintendent of the National Fire Academy and had asked him what 
training did FFs get at NFA on automatic fire protection systems..."limited at 
best".  Garbage in, garbage out as for the NFIRS field data.  NFPA's advertised 
statistics are based on these 2am fire fighter reports not on a professional 
experienced examination or inspection.

I've trained a few fire fighters (on fixed suppression) and a few fire 
inspectors and can attest for their lack of required knowledge and experience.  
I recently reviewed the DOD fire inspector I course; and well, there's just not 
much in there.

There is a reluctance from the trade to publish negative stories, its a form of 
confirmation bias.  Virtually all of the trade press (Sprinkler Quarterly, 
Sprinkler Age, BAFSA) actively solicit "success stories" not failure stories.  
They should adopt a negative feedback position and solicit the opposite.  We 
learn from the failures of others, not from hearing the same "sales" pitch over 
and over again.  Shame on the industry for repeating the same statistics -we 
learn nothing from that press, nothing.  It's self-serving BS to make us feel 
good. Until such time as the trade stops being salemen I won't take them at 
their word.

Last I recall Denver was requiring the use of "modeled" hydraulic data. When I 
was contracting there in the early 2000s I recall there was pressure to accept 
modeled flow test data from Denver Water and a reluctant to do true blue NFPA 
291 (a/k/a Prof. Pat Brock style) proper flow testing.  Who verified or 
verifies the model outputs?  How frequently is that model tested with real work 
data.

The NFPA system is very slow to take negative feedback and adjust the 
standards, in theory it works but its painfully slow.  It would help if the 
press would stop playing salesman.  Make one snide comment about "minimums" and 
NFPA 13 and see what happens on the forum.  Those responders are virtually all 
designers sitting in their offices.

As for as-builts.  Overseas they're all rubber stamped after the fact.  
As-builts rarely reflect reality.  Acceptance/commissioning is a farce overseas.

All the best

Byron
Diego Garcia, BIOT





________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Scott Futrell <[email protected]>
Sent: Monday, June 18, 2018 5:16 AM
To: [email protected]
Subject: RE: Safety Margin


Ron,



We’ll need to talk about these so called statistics that come from incomplete 
and inaccurate NFIRS reports almost exclusively.  I’ve researched the 
statistics, spoken with NFPA, and I can tell you the statistics are only as 
accurate as the firefighters writing them at the time of the fire. 
Investigations go on for months longer and NFIRS reports are rarely updated. 
Currently NFPA states that 97% of fires are controlled by 5 sprinklers or less, 
so that is up from what it used to be.



I can assure you that many of the fires I investigate, that have sprinklers 
that were ineffective are not accurately or not included in those statistics. 
$35M fire in Illinois recorded as less than $10M and didn’t make the NFPA large 
loss fires.  Sprinklered. Sprinklered part of the building burned to the 
ground…none of that made NFPA investigation or statistics.



I have pictures, reports, NFIRS reports and more to back this up and my files 
grow weekly.



I recently had an interesting debate with a NICET designer from Denver. I told 
her the flow test was wrong (it is of course), the pump test was incorrect and 
old (it is of course) and she hadn’t as-built the BFP on the plans correctly 
that her company replaced.  She told me “she didn’t have time to drive the two 
hours to Denver to verify the as-built conditions” and that was the flow test 
the city gave them (incorrect side of the building, old, and off larger main 
than the pump suction). The supposed safety margin she was providing was 
non-existent.  I realize this story isn’t reflective of requirements for a 
safety margin, but it is reflective of an improperly designed system that will 
be just fine until we have a fire and then we find out it wasn’t.



I have many design related stories and my plan review rate remains at >70% 
revise and resubmit with the majority of the problems water supply and 
hydraulic calculation related.



I have a NFIRS report in my hands that states that the sprinklers 
operated/ineffective and that three operated.  There were more than three that 
operated, but more importantly the two branch lines directly over the area of 
origin were capped without a water supply to those sprinklers!!!



Take care my friend.



Scott



Office: (763) 425-1001 x2

Cell: (612) 759-5556



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ron Greenman
Sent: Saturday, June 16, 2018 11:25 AM
To: [email protected]
Subject: Re: Safety Margin



Where is the data that supports the need? I don't have the exact numbers in my 
head this morning, nor am I willing to look them up but the statistics are that 
somewhere above 90% of all fires are controlled by a single or two sprinklers 
operating, and above 95% are controlled by three (anybody jump in with the 
exact numbers), and since we design to nine or usually more typically I'd say a 
safety factor is already built-in. I think if you look at systems that have 
been overwhelmed you'll mostly find that maintenance was not carried out 
properly, or TIs were not addressed, or fires got into unsprinklered or under 
sprinklered attics, or any number of things that were existing code deficient. 
I also think you'd find that many fires were controlled by systems that were 
existing code deficient. My mind could be changed if I were shown a significant 
amount of loss due to inadequate water in the original design in buildings 
where there were no other factors as stated above, but I'm not seeing a need. 
Additionally, in my neck of the woods, all the metropolitan jurisdictions are 
already imposing a 10# or 10% factor already. Most are holding to that number 
like it's gold and even if the hose stream allowance takes you over the supply 
line by 1/2# you're surely going to have to re-design. This is unreasonable 
already, and I realize the FDs already often act like over-indulgent parents, 
so I'm especially worried that if this 10#s is codified it will be an add-on to 
the already existent 10#s. I see tanks and pumps in everyone's future because 
of mistrust of municipal water systems. Rant over. Ron out.





Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700



The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)





On Sat, Jun 16, 2018 at 7:50 AM Scott Futrell 
<[email protected]<mailto:[email protected]>> wrote:

As a plan specifier, plan reviewer and an investigator I see designs right to 
the supply and then as-built conditions far worse (read more demanding) than 
the design submitted with the calcs.  This is not a regional observation.



Additionally, I am aware of communities that lower elevated tank levels 20’ in 
winter to lower heating costs.  Contractors in those areas do NOT adjust flow 
tests for this seasonal variation.



No safety margin what-so-ever in NFPA 13 is unreasonable for a design standard.



Arguments on the floor including ‘requiring all systems to have back-up power’ 
were ridiculous.



Scott



Office: (763) 425-1001 x2

Cell: (612) 759-5556



From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Steve Leyton
Sent: Friday, June 15, 2018 2:16 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Safety Margin



That was the conversation on the floor of the code hearing.  The concerns 
underscored by the CAM were not about whether safety factor is a good practice, 
it was that a fixed minimum value as high as 10 PSI could trigger all sorts of 
cost-impact consequences, particularly in areas where pressures are middling to 
poor – in Rhode Island, 10 PSI could be 25-30% of the available pressure.



In the West, due primarily to the politics of drought, water districts are 
using models in lieu of physical flow tests.  Prudent and conservative 
programming makes it possible for them to issue safeguarded values from which 
it’s not necessary to reduce the available pressure.  For ex., City of San 
Diego uses a three-level safety factor in their (highly accurate) models:  
starting with legacy drought water levels in the reservoirs, then factor the 
highest seasonal demand, then the highest peak day demand of that season.   The 
values we’re getting are usually significantly lower than what can be measured 
on the hydrant, and this practice isn’t without controversy because there are 
obvious complications that can and do occur, particularly with existing systems 
based on 20-year old (and older) pressures that were physically measured (with 
crappy equipment) when first designed and built.



But if modeling becomes the new normal, prudent water district engineering 
departments and fire departments they serve can coordinate manipulating data to 
include reasonable safety factors.  The range of variation in pressures, 
accuracy of flow test equipment, the use of modeling in many areas … there are 
too many variables to set a fixed minimum safety factor based on PSI, IMHO.



SML



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Friday, June 15, 2018 12:00 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Safety Margin



Richard,

If my memory is accurate of the issues raised in the discussion that ambiguity 
was a part of the differing viewpoints.

Some argued that 10 psi was not workable in their locale as their pressures 
were so limited that an imposition of 10 psi was simply to drastic and would 
result in much larger pipe sizes as a result.

Others argued that 10 psi was not enough, and in their area 10 psi didn't equal 
10%, and there was some reluctance to base their designs on a pressure greater 
than 90% of the available.

It was quite a discussion.

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>

On 06/15/2018 10:23 AM, Richard Carr wrote:

Even though it is not in NFPA most AHJ’s require some sort of safety margin, 
10%, 10 psi which we have had to provide for a long time so most designers know 
to leave safety margin in the calc’s. it would be nice if they all used the 
same amount.



Richard M. Carr, SET

Project Manager/Design

Diboco Fire Sprinklers, Inc.

325 Jackson Loop Road

Flat Rock, NC  28731



[email protected]<mailto:[email protected]>

828-696-3400

828-696-2288 Fax

828-708-9118 Mobile



[cid:[email protected]]



[cid:[email protected]]





From: Sprinklerforum 
<[email protected]><mailto:[email protected]>
 On Behalf Of Parsley Consulting
Sent: Friday, June 15, 2018 1:22 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Safety Margin



Scott,

Based on the material which was presented to the -24 and -291 committee 
meetings I believed the proposed safety margin and the means to calculate that 
margin there was some merit in the proposal.

For reasons I don't quite remember the PI was voted down at the 2nd draft 
meeting.  I listened to some of the discussion, and there were some good points 
made.  I'm not terribly surprised it failed at the convention level.  Perhaps 
the attendees were following the lead of the technical committees, and 
declining to overrule their decision.

sincerely,

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>

On 06/15/2018 8:09 AM, Scott Futrell wrote:

Only that the 'safety margin' inclusion in the 2019 edition of NFPA 13 failed, 
so it won't be included or required.



I consider this unfortunate, but I'd guess that not everyone on the forum would 
agree.



Scott



Office: (763) 425-1001 x2

Cell: (612) 759-5556



-----Original Message-----

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>

Sent: Thursday, June 14, 2018 5:46 PM

To: 
[email protected]<mailto:[email protected]>

Subject: NFPA Vegas Convention



I didn't make it again this year.

"Caputo" is the only speaker name I recognized.

Anybody have any earthshaking epiphanies?





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to