It sort of matters; think firefighters flaking out no less than 100-feet of 
hose (maybe more) in the stairwell before charging the hose line with standpipe 
water.  This has to be laid neatly so it does tangle and kink on charging.  
Typically the FD will hook to the first outlet BELOW the level of the fire, but 
then lay ½ of the hose up the stair above the fire, then come back down, to 
make entry on fire floor (laying hose above so it's easier to pull into the 
floor as they are crawling along).  Hooking below is so if things go really 
bad, the firefighters can hands on follow the hose out into the stairway and 
down, hopefully to a safer place.

The half-level provides for more hose reach into the actual floor.

Andrew Steele


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trever Williams
Sent: Tuesday, September 11, 2018 1:35 PM
To: [email protected]
Subject: Hose Connections - Main Stair Landings vs. Intermediate Landings

>From a practical standpoint does it matter if the hose connections in the 
>stairwells are installed on the main floor landings or the intermediate 
>landings?

I remember learning years ago that it really doesn't matter, and in a fully 
sprinkled building it really, really doesn't matter, but lately I've been 
encountering AHJs that seem to think it matters.

Trever Williams
Design Manager
Unlimited Sprinkler Fire Protection
130 Kristen Ln.
Wylie, TX 75098
214-349-8444 ex. 312 - Phone
214-349-8450 - Fax