At the end of the day we always install the hose connections the way the fire 
departments want them.

Most of the fire code officials I’ve worked with over the years have been fine 
with exercising their option to allow the hose connections to be installed on 
the main floor landings.  But lately I’ve worked with a few who seem think it 
is vitally important that the hose connections be installed on the intermediate 
landings, and I don’t think that’s true.

The perceived benefits from our side aren’t completely irrelevant to the 
serving fire department when you look at the bigger picture.  If fire 
departments are going to enforce policies that increase the cost fire 
protection systems it should be for things that significantly increase the life 
safety aspects of the systems.  Forcing building owners to install the hose 
connections on the intermediate landings when it is much more cost effective to 
install them on the floor landings doesn’t do that.

Trever Williams
Design Manager
Unlimited Sprinkler Fire Protection
130 Kristen Ln.
Wylie, TX 75098
214-349-8444 ex. 312 - Phone
214-349-8450 - Fax

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, September 13, 2018 10:36 AM
To: [email protected]
Subject: Re: Hose Connections - Main Stair Landings vs. Intermediate Landings

Believe me, firefighters today are trained for just about any eventuality. 
Think about it: over the course of many years standpipe systems in many cities 
have been designed and built with connections on both ends of the stairwells. 
They've been built across at least 2 generations of the standard with different 
discharge pressures.  There are fire departments in older cities that carry 3 
sets of tips so they can work with higher to lower pressures as conditions 
require.   The perceived benefits from our side of the counter may be valid but 
they are irrelevant to the serving fire department. Whatever they want is what 
should be required
Steve Leyton
(Sent from my smart phone, so please excuse typos and voice-to-text 
corruptions.)

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Trever Williams <[email protected]>
Sent: Thursday, September 13, 2018 9:05:07 AM
To: [email protected]
Subject: RE: Hose Connections - Main Stair Landings vs. Intermediate Landings

I can see subtle benefits for doing it either way, but the benefits seem so 
minor that it really shouldn’t matter.  It seems like the fire departments 
should have training and operational tactics for both situations.  Different 
jurisdictions do it different ways and they could find themselves lending 
support to a jurisdiction that does it the opposite way.

Trever Williams
Design Manager
Unlimited Sprinkler Fire Protection
130 Kristen Ln.
Wylie, TX 75098
214-349-8444 ex. 312 - Phone
214-349-8450 - Fax

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, September 12, 2018 12:54 PM
To: [email protected]
Subject: RE: Hose Connections - Main Stair Landings vs. Intermediate Landings

What Bruce said.  Both Code (intermediates) and Standard (floors) state what 
they state but also contain a provision that essentially says, “Or as required 
by the fire official…”   If you have any doubt, consult with and affirm the 
locations with the fire official.

I personally like the floor landings because it makes the floor control 
assemblies and drains easier on combined systems and most FDs we work with in 
the Southwest specify floor landings.  But we have more than a few that prefer 
the intermediates; this goes to department training practices and operational 
tactics so deference to the FD’s preference is paramount.

My 2¢ only,

[Steve Signature (3)]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bruce Verhei
Sent: Tuesday, September 11, 2018 2:00 PM
To: [email protected]
Subject: Re: Hose Connections - Main Stair Landings vs. Intermediate Landings

I’d contact local FD and see their requirements.

Floor below was long tradition. Dates back to standpipes being inserted into 
stairwell. Now you’re normally in a rated shaft. You don’t need a hose line to 
follow once you’re in the rated stairwell.

Best.

Bruce Verhei

On Sep 11, 2018, at 10:39, Steele, Andrew 
<[email protected]<mailto:[email protected]>> wrote:
It sort of matters; think firefighters flaking out no less than 100-feet of 
hose (maybe more) in the stairwell before charging the hose line with standpipe 
water.  This has to be laid neatly so it does tangle and kink on charging.  
Typically the FD will hook to the first outlet BELOW the level of the fire, but 
then lay ½ of the hose up the stair above the fire, then come back down, to 
make entry on fire floor (laying hose above so it’s easier to pull into the 
floor as they are crawling along).  Hooking below is so if things go really 
bad, the firefighters can hands on follow the hose out into the stairway and 
down, hopefully to a safer place.

The half-level provides for more hose reach into the actual floor.

Andrew Steele


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trever Williams
Sent: Tuesday, September 11, 2018 1:35 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Hose Connections - Main Stair Landings vs. Intermediate Landings

From a practical standpoint does it matter if the hose connections in the 
stairwells are installed on the main floor landings or the intermediate 
landings?

I remember learning years ago that it really doesn’t matter, and in a fully 
sprinkled building it really, really doesn’t matter, but lately I’ve been 
encountering AHJs that seem to think it matters.

Trever Williams
Design Manager
Unlimited Sprinkler Fire Protection
130 Kristen Ln.
Wylie, TX 75098
214-349-8444 ex. 312 - Phone
214-349-8450 - Fax


________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to