If course. FDC threads damaged. Grab double female, and pump into ground floor 
outlet. 

> On Sep 13, 2018, at 08:35, Steve Leyton <[email protected]> wrote:
> 
> Believe me, firefighters today are trained for just about any eventuality. 
> Think about it: over the course of many years standpipe systems in many 
> cities have been designed and built with connections on both ends of the 
> stairwells. They've been built across at least 2 generations of the standard 
> with different discharge pressures.  There are fire departments in older 
> cities that carry 3 sets of tips so they can work with higher to lower 
> pressures as conditions require.   The perceived benefits from our side of 
> the counter may be valid but they are irrelevant to the serving fire 
> department. Whatever they want is what should be required
> 
> Steve Leyton
> (Sent from my smart phone, so please excuse typos and voice-to-text 
> corruptions.)
> 
>  
> From: Sprinklerforum <[email protected]> on 
> behalf of Trever Williams <[email protected]>
> Sent: Thursday, September 13, 2018 9:05:07 AM
> To: [email protected]
> Subject: RE: Hose Connections - Main Stair Landings vs. Intermediate Landings
>  
> I can see subtle benefits for doing it either way, but the benefits seem so 
> minor that it really shouldn’t matter.  It seems like the fire departments 
> should have training and operational tactics for both situations.  Different 
> jurisdictions do it different ways and they could find themselves lending 
> support to a jurisdiction that does it the opposite way.
>  
> Trever Williams
> Design Manager
> Unlimited Sprinkler Fire Protection
> 130 Kristen Ln.
> Wylie, TX 75098
> 214-349-8444 ex. 312 - Phone
> 214-349-8450 - Fax
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Leyton
> Sent: Wednesday, September 12, 2018 12:54 PM
> To: [email protected]
> Subject: RE: Hose Connections - Main Stair Landings vs. Intermediate Landings
>  
> What Bruce said.  Both Code (intermediates) and Standard (floors) state what 
> they state but also contain a provision that essentially says, “Or as 
> required by the fire official…”   If you have any doubt, consult with and 
> affirm the locations with the fire official.
>  
> I personally like the floor landings because it makes the floor control 
> assemblies and drains easier on combined systems and most FDs we work with in 
> the Southwest specify floor landings.  But we have more than a few that 
> prefer the intermediates; this goes to department training practices and 
> operational tactics so deference to the FD’s preference is paramount.
>  
> My 2¢ only,
>  
> <image001.png>
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Bruce Verhei
> Sent: Tuesday, September 11, 2018 2:00 PM
> To: [email protected]
> Subject: Re: Hose Connections - Main Stair Landings vs. Intermediate Landings
>  
> I’d contact local FD and see their requirements.
>  
> Floor below was long tradition. Dates back to standpipes being inserted into 
> stairwell. Now you’re normally in a rated shaft. You don’t need a hose line 
> to follow once you’re in the rated stairwell.
>  
> Best.
>  
> Bruce Verhei 
> 
> On Sep 11, 2018, at 10:39, Steele, Andrew <[email protected]> 
> wrote:
> 
> It sort of matters; think firefighters flaking out no less than 100-feet of 
> hose (maybe more) in the stairwell before charging the hose line with 
> standpipe water.  This has to be laid neatly so it does tangle and kink on 
> charging.  Typically the FD will hook to the first outlet BELOW the level of 
> the fire, but then lay ½ of the hose up the stair above the fire, then come 
> back down, to make entry on fire floor (laying hose above so it’s easier to 
> pull into the floor as they are crawling along).  Hooking below is so if 
> things go really bad, the firefighters can hands on follow the hose out into 
> the stairway and down, hopefully to a safer place.
>  
> The half-level provides for more hose reach into the actual floor.
>  
> Andrew Steele
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Trever Williams
> Sent: Tuesday, September 11, 2018 1:35 PM
> To: [email protected]
> Subject: Hose Connections - Main Stair Landings vs. Intermediate Landings
>  
> From a practical standpoint does it matter if the hose connections in the 
> stairwells are installed on the main floor landings or the intermediate 
> landings?
>  
> I remember learning years ago that it really doesn’t matter, and in a fully 
> sprinkled building it really, really doesn’t matter, but lately I’ve been 
> encountering AHJs that seem to think it matters.
>  
> Trever Williams
> Design Manager
> Unlimited Sprinkler Fire Protection
> 130 Kristen Ln.
> Wylie, TX 75098
> 214-349-8444 ex. 312 - Phone
> 214-349-8450 - Fax
>  
>  
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to