In making an informed decision on our next step, we are considering the
head change out and pilot PRVs.
Questions:
1. If we install PRVs, don't need high pressure heads (and probably visa
versa), right?
2. Are all high pressure heads the glass bulb type and do bulb type
heads require testing every 5 yrs starting with year 20?
3. Are all PRVs flange mounted?
Thanks
-------- Forwarded Message --------
Subject: RE: High Pressure Sprinklers
Date: Sat, 15 Sep 2018 15:02:07 +0000
From: John Corcoran <[email protected]>
Reply-To: [email protected]
To: [email protected]
<[email protected]>
Same sprinklers as the 175psi, but tested at higher pressure.
I can only speak for Globe, but I believe other manufacturers are the same.
https://globesprinkler.com/product-category/s7-high-pressure#quickresponse
https://globesprinkler.com/product-category/s7-high-pressure#standardresponse
*John Corcoran*
Senior Communications Manager
globesprinkler.com
*E*[email protected]
*P*989.414.2251
*F*989.846.9231
*From:*Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Ron Greenman
*Sent:* Saturday, September 15, 2018 10:31 AM
*To:* [email protected]
*Subject:* High Pressure Sprinklers
On a different thread Ben Young made a comment about using higher
pressure sprinklers. Does anyone know if these sprinklers are actually
different from the standard 175psi sprinklers or do they the same
sprinklers that have just met a more demanding UL/FM testing protocol?
Ron Greenman
[email protected] <mailto:[email protected]>
253.576.9700
The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
---