20 years testing isn't due to the glass bulb it's due to the heads being
quick response. You can get standard response heads with bulbs that will
last another fifty years.

Check this head out:
https://www.reliablesprinkler.com/sites/default/files/products/bulletins/013.pdf

This is an SR bulb head that has it's 1/2" version listed to 250 psi
instead of the standard 175. I see that as a nice value added feature for
no extra cost, but that's just me.

On Sat, Sep 15, 2018 at 11:31 AM Steward- Larry <[email protected]>
wrote:

> In making an informed decision on our next step, we are considering the
> head change out and pilot PRVs.
>
> Questions:
> 1. If we install PRVs, don't need high pressure heads (and probably visa
> versa), right?
> 2. Are all high pressure heads the glass bulb type and do bulb type heads
> require testing every 5 yrs starting with year 20?
> 3. Are all PRVs flange mounted?
>
> Thanks
>
> -------- Forwarded Message --------
> Subject: RE: High Pressure Sprinklers
> Date: Sat, 15 Sep 2018 15:02:07 +0000
> From: John Corcoran <[email protected]>
> <[email protected]>
> Reply-To: [email protected]
> To: [email protected]
> <[email protected]>
> <[email protected]>
>
> Same sprinklers as the 175psi, but tested at higher pressure.
>
> I can only speak for Globe, but I believe other manufacturers are the
> same.
>
>
>
> https://globesprinkler.com/product-category/s7-high-pressure#quickresponse
>
>
> https://globesprinkler.com/product-category/s7-high-pressure#standardresponse
>
>
>
>
>
> *John Corcoran*
>
> Senior Communications Manager
>
> globesprinkler.com
>
> *E* [email protected]
> *P* 989.414.2251
> *F* 989.846.9231
>
>
>
>
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Ron
> Greenman
> *Sent:* Saturday, September 15, 2018 10:31 AM
> *To:* [email protected]
> *Subject:* High Pressure Sprinklers
>
>
>
> On a different thread Ben Young made a comment about using higher pressure
> sprinklers. Does anyone know if these sprinklers are actually different
> from the standard 175psi sprinklers or do they the same sprinklers that
> have just met a more demanding UL/FM testing protocol?
>
>
>
>
>
> Ron Greenman
>
>
> [email protected]
>
> 253.576.9700
>
>
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
>  Virus-free.
> www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
> <#m_3994104601826112497_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 

Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to