I have another question. I know it is a lot with all these Larry’s running 
around.

When I started my thread, I mentioned that we have had no corrosion on the 
cap/orifice area. Turns out that on the head replacement job we are just 
finishing up (and unlike the last job we did next door in the same riser 
system), some of these demo’d heads do have considerable corrosion on the cap 
and orifice area. Maybe 2-3%. Is that caused by leakage or is more insidious? 
Thanks.

Larry B


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Saturday, September 15, 2018 9:06 AM
To: [email protected]; [email protected]
Subject: Re: RE: High Pressure Sprinklers

20 years testing isn't due to the glass bulb it's due to the heads being quick 
response. You can get standard response heads with bulbs that will last another 
fifty years.

Check this head out:
https://www.reliablesprinkler.com/sites/default/files/products/bulletins/013.pdf

This is an SR bulb head that has it's 1/2" version listed to 250 psi instead of 
the standard 175. I see that as a nice value added feature for no extra cost, 
but that's just me.

On Sat, Sep 15, 2018 at 11:31 AM Steward- Larry <[email protected]> 
wrote:
In making an informed decision on our next step, we are considering the head 
change out and pilot PRVs.

Questions:
1. If we install PRVs, don't need high pressure heads (and probably visa 
versa), right?
2. Are all high pressure heads the glass bulb type and do bulb type heads 
require testing every 5 yrs starting with year 20?
3. Are all PRVs flange mounted?

Thanks

-------- Forwarded Message --------

Subject:
RE: High Pressure Sprinklers

Date:
Sat, 15 Sep 2018 15:02:07 +0000

From:
John Corcoran  <mailto:[email protected]> 
<[email protected]>

Reply-To:
[email protected]

To:
[email protected]  
<mailto:[email protected]> 
<[email protected]>

Same sprinklers as the 175psi, but tested at higher pressure.
I can only speak for Globe, but I believe other manufacturers are the same.

https://globesprinkler.com/product-category/s7-high-pressure#quickresponse
https://globesprinkler.com/product-category/s7-high-pressure#standardresponse



John Corcoran
Senior Communications Manager
globesprinkler.com
E [email protected]
P 989.414.2251
F 989.846.9231




From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ron Greenman
Sent: Saturday, September 15, 2018 10:31 AM
To: [email protected]
Subject: High Pressure Sprinklers

On a different thread Ben Young made a comment about using higher pressure 
sprinklers. Does anyone know if these sprinklers are actually different from 
the standard 175psi sprinklers or do they the same sprinklers that have just 
met a more demanding UL/FM testing protocol?



Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
 www.avast.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--

Benjamin Young


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org