Mr. Ben
As per 2016 edition of NFP13, clause 8.15.2/8.15.3 can be refered, which
calls for Vertical shafts/Stairways and defines the sprinkler requirement
for combustible / non-combustible /limited combustible shafts and further
8.15.3.1 states "Combustible Construction. Sprinklers shall be installed
beneath all stairways of combustible construction." and  8.15.3.2.2, calls
for sprinkler protection  " Where noncombustible stair shafts are divided
by walls or doors, sprinklers shall be provided on each side of the
separation."



On Fri, Sep 21, 2018 at 5:03 PM Ben Young <[email protected]> wrote:

> I'm curious to see how the rest of the people on the forum handle
> protection at the top of the stair shaft, as we have an internal debate in
> our office.
>
> The 2007 edition of the NFPA 13 handbook has an exhibit, 8.29, which is on
> page 334, and is involved with 8.15.3.2.1 in the 2007 edition.
>
> If you're not familiar with the picture, I'll see if I can get a scan, but
> its basically a cross section of a stair tower, and has two circled letters
> on it: B under the lowest intermediate landing, and A above the top main
> floor landing.
>
> Basically this Exhibit and the explanatory handbook text after 8.15.3.2.1
> implies that the head at the top of a non-combustible stair shaft is only
> to protect the top floor landing, and NOT the entire footprint of the stair
> tower itself.
>
> So under this code, the interpretation was that you could protect a 24x10
> foot large stair tower with only two standard spray heads.
>
> Does anyone else feel this is appropriate? Or how do you feel about the
> code/handbook change and the nuance behind this situation.
>
> I will start with the discussion by saying that I see the appeal of only
> installing the one head over the top floor landing as installing another
> head at the top over the intermediate landings can often be difficult to do
> off ladders, especially if its a very tall stair tower.
>
> I also can also understand that from an AHJ perspective, 'sprinklers
> installed at the top of the shaft' in the code language would be
> conservatively read as the ENTIRE top.
>
> What are your thoughts?
>
> Thanks,
> Ben Young
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to