I have a 3 story living condo.
There are 4 units which each have an open parking garage under the 2nd floor. Along the back wall are 4 (10sqft ) closets. The engineer is asking for a dry system designed to .15/1950. Just want to know what everyone's thoughts are about not including the sprinklers in these closets. Using the provision 23.4.4.6.2 It would allow me to eliminate 14 sprinklers from my calculation area. Regards Troy