Kyle,

Refer to NFPA-13, 2016 Ed, page 52, parag. 8.4.6.6.  This may apply to your
situation.

John O'Connor

National Fire Sprinklers, Inc.

Nashville TN

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Kyle.Montgomery
Sent: Monday, October 08, 2018 3:26 PM
To: [email protected]
Subject: Converting from ESFR to CMDA - Spacing Issues

 

We're looking at a project where a portion of an existing ESFR building is
being converted to store cartooned expanded plastics. It looks like we've
settled on a design criteria that involves changing out the sprinklers at
the deck to 11.2K standard spray sprinklers at a 0.45 density and adding 2
levels of in-rack sprinklers.

 

This issue I need to address is this: Existing ESFR sprinklers took
advantage of the spacing allowance to avoid being obstructed by structural
members. The lines are 10 ft on-center and the head spacing is 10, 10, 9,
11, 10, 10, 9, 11.

 

The new upright sprinklers are limited to 100 square foot maximum spacing.
Is there any good option/allowance where we could just replace the heads and
keep the spacing? Or are we going to need to relocate every fourth head to
maintain 10-foot spacing all the way down the branch line.

 

I'm pretty sure FM Global allows for this, but I haven't found anything in
NFPA 13 outside of the ESFR section. It sure seems like if it's appropriate
for ESFR heads (arguably the most finicky with regard to
spacing/obstructions) that the same spacing should be OK for standard spray
sprinklers.

 

Kyle Montgomery

 cid:[email protected]

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

 <mailto:[email protected]> [email protected]

 

 


 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_cam
paign=sig-email&utm_content=emailclient> 

Virus-free.
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_cam
paign=sig-email&utm_content=emailclient> www.avg.com 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to