Thanks, John, but it's still a storage occupancy, just a different 
commodity/arrangement than what we can protect with ESFR sprinklers.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John O'Connor
Sent: Tuesday, October 9, 2018 12:05 PM
To: [email protected]
Subject: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

Kyle,
Refer to NFPA-13, 2016 Ed, page 52, parag. 8.4.6.6.  This may apply to your 
situation.
John O'Connor
National Fire Sprinklers, Inc.
Nashville TN

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Monday, October 08, 2018 3:26 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Converting from ESFR to CMDA - Spacing Issues

We're looking at a project where a portion of an existing ESFR building is 
being converted to store cartooned expanded plastics. It looks like we've 
settled on a design criteria that involves changing out the sprinklers at the 
deck to 11.2K standard spray sprinklers at a 0.45 density and adding 2 levels 
of in-rack sprinklers.

This issue I need to address is this: Existing ESFR sprinklers took advantage 
of the spacing allowance to avoid being obstructed by structural members. The 
lines are 10 ft on-center and the head spacing is 10, 10, 9, 11, 10, 10, 9, 
11...

The new upright sprinklers are limited to 100 square foot maximum spacing. Is 
there any good option/allowance where we could just replace the heads and keep 
the spacing? Or are we going to need to relocate every fourth head to maintain 
10-foot spacing all the way down the branch line.

I'm pretty sure FM Global allows for this, but I haven't found anything in NFPA 
13 outside of the ESFR section. It sure seems like if it's appropriate for ESFR 
heads (arguably the most finicky with regard to spacing/obstructions) that the 
same spacing should be OK for standard spray sprinklers.

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>


[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.avg.com_email-2Dsignature-3Futm-5Fmedium-3Demail-26utm-5Fsource-3Dlink-26utm-5Fcampaign-3Dsig-2Demail-26utm-5Fcontent-3Demailclient&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=fvTD_NBvyGYjQ9mLbSfDI5w_Q7y5ajqPy12Jf7wVdrk&s=8cBOJ505izCf6Af0ivAGkMTfp5T6bxEIRLaOHTPZIUU&e=>

Virus-free. 
www.avg.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.avg.com_email-2Dsignature-3Futm-5Fmedium-3Demail-26utm-5Fsource-3Dlink-26utm-5Fcampaign-3Dsig-2Demail-26utm-5Fcontent-3Demailclient&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=fvTD_NBvyGYjQ9mLbSfDI5w_Q7y5ajqPy12Jf7wVdrk&s=8cBOJ505izCf6Af0ivAGkMTfp5T6bxEIRLaOHTPZIUU&e=>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to