I have an attic that has 2, 24' deep x 86' wide areas. so in those areas I have 
to use standard spray sprinkler because attic sprinkler haven't been tested 
beyond 80' according to the data sheet. Most of the rest of the attic is 63'-2" 
wide and under normal circumstances I would use a row of BB' at the peak and a 
row of AP at each eave. Question is, is there any reason I couldn't use 
standard in the 86' wide areas and attic sprinklers everywhere else.