Richard, you can do what you are thinking.  You will have multiple calc areas 
and will have to do a mixed calc area, 2,535 sf with both B2B and SSU 
sprinklers.  TYCO’s data sheet explains all of this.  If you have a decent 
water supply you shouldn’t have any real issues.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Friday, October 12, 2018 5:05 PM
To: [email protected]
Subject: Attic Sprinklers

 

I have an attic that has 2, 24' deep x 86' wide areas. so in those areas I have 
to use standard spray sprinkler because attic sprinkler haven't been tested 
beyond 80' according to the data sheet. Most of the rest of the attic is 63'-2" 
wide and under normal circumstances I would use a row of BB' at the peak and a 
row of AP at each eave. Question is, is there any reason I couldn't use 
standard in the 86' wide areas and attic sprinklers everywhere else. 

 