Yes.  If occupied, I would say it is not an attic any longer.  If there is no 
ceiling, it is not a concealed space.  These are specially listed concealed 
space sprinklers.  A call to Tyco technical services would clear it up for you 
if that is not enough.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum <[email protected]> On Behalf 
Of [email protected]
Sent: Friday, June 28, 2019 10:37 AM
To: [email protected]
Subject: RE: Attic sprinklers

If it’s ‘occupied’, is it still considered an attic?

Cliff Whitfield, SET
President

Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772

[Description: New FDI Logo-4.jpg]

From: Sprinklerforum <[email protected]> On Behalf 
Of Fpdcdesign
Sent: Friday, June 28, 2019 1:34 PM
To: Sprinklerforum <[email protected]>
Subject: Attic sprinklers

Where in NFPA 13 or in their listings are attic sprinklers restricted to 
unoccupied attic spaces?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)

[Image removed by 
sender.]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to