I agree. Check valves are required.

John

John August Denhardt, P.E.
Strickland Fire Protection

On Nov 6, 2018, at 3:41 PM, Mike Stossel 
<[email protected]<mailto:[email protected]>> wrote:

If I am understanding you question correctly, check valves are required.

8.16.1.5 Floor Control Valve Assemblies.
8.16.1.5.1* Multistory buildings exceeding two stories in height shall be 
provided with a floor control valve, check valve, main drain valve, and flow 
switch for isolation, control, and annunciation of water flow on each floor 
level.

Mike Stossel SET
<image002.png>
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Fpdcdesign
Sent: Tuesday, November 6, 2018 3:38 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Back to back floor controls.

I am working on an existing two story plus attic wood frame building. The 
engineer is requiring zone control assemblies (butterfly valve plus riser 
manifold) for every level including the attic. I have designed it so there is a 
bull head tee at the top of a 4” riser with the assemblies on either side of 
the tee. Given that the flow switches are going to be in close proximity, 
should I install a check valve between the butterfly valve and the manifold?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to