Hi Steve,
Occasionally you and I see things differently, but on this, my friend we are in 
100% agreement.  Well said.

Mark at Aero
602 820-7894

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, November 6, 2018 10:32 PM
To: [email protected]
Subject: [EXTERNAL] Re: Back to back floor controls.

You know, at some point we have to stop being sheep and take the initiative. I 
understand that the designer is subordinate to the directive of the engineer of 
record.  But in this case the EOR is recommending something that I passionately 
and organically believe to be a bad practice. Installing unnecessary control 
valves adds potential failure links to the chain of events. Plus unnecessary 
first cost and unnecessary ongoing cost for maintenance of these redundant 
valves and supervisory devices.

Someday, if one of those valves gets left shut and the system fails to control 
or suppress a fire, and heaven forbid somebody should be injured or killed, the 
designer and everyone else associated with the project will get sued. There is 
no good reason to add those valves to system configured as described. Talking 
about whether check valves or flow switches are required just adds to the level 
of obscuration. To me the issue should be how best to stand up to the idiot who 
is specifying this arrangement.


Steve Leyton

(Sent from my phone; please excuse typos and voice text corruptions.)



-------- Original message --------
From: John Denhardt 
<[email protected]<mailto:[email protected]>>
Date: 11/6/18 11:49 PM (GMT+03:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Back to back floor controls.

I agree. Check valves are required.

John
John August Denhardt, P.E.
Strickland Fire Protection

On Nov 6, 2018, at 3:41 PM, Mike Stossel 
<[email protected]<mailto:[email protected]>> wrote:
If I am understanding you question correctly, check valves are required.

8.16.1.5 Floor Control Valve Assemblies.
8.16.1.5.1* Multistory buildings exceeding two stories in height shall be 
provided with a floor control valve, check valve, main drain valve, and flow 
switch for isolation, control, and annunciation of water flow on each floor 
level.

Mike Stossel SET
<image002.png>
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Fpdcdesign
Sent: Tuesday, November 6, 2018 3:38 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Back to back floor controls.

I am working on an existing two story plus attic wood frame building. The 
engineer is requiring zone control assemblies (butterfly valve plus riser 
manifold) for every level including the attic. I have designed it so there is a 
bull head tee at the top of a 4" riser with the assemblies on either side of 
the tee. Given that the flow switches are going to be in close proximity, 
should I install a check valve between the butterfly valve and the manifold?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=AKRiqOJP41XYwX8V63Z7k1sq-QF9pscYmMfZpODbrYM&s=e20UzOalQKovft1L40sJRl9vCkN0c5bGsdoLNh8rJYg&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to