I thought Todd said this was a 2-story building?


I’d use the check valves but more for good ‘engineering practice’.  I’m not 
certain that they are ‘required’, based on the info Todd provided.



Just my opinion.



Cliff Whitfield, SET

President



Fire Design, Inc.

184 Comfort Place

Burnsville, NC 28714

Ph: 828-284-4772







 <mailto:[email protected]> [email protected]

 <http://www.fire-design.com/> www.fire-design.com



From: Sprinklerforum <[email protected]> On Behalf 
Of John Denhardt
Sent: Tuesday, November 6, 2018 3:49 PM
To: [email protected]
Subject: Re: Back to back floor controls.



I agree. Check valves are required.



John

John August Denhardt, P.E.

Strickland Fire Protection


On Nov 6, 2018, at 3:41 PM, Mike Stossel <[email protected] 
<mailto:[email protected]> > wrote:

If I am understanding you question correctly, check valves are required.



8.16.1.5 Floor Control Valve Assemblies.

8.16.1.5.1* Multistory buildings exceeding two stories in height shall be 
provided with a floor control valve, check valve, main drain valve, and flow 
switch for isolation, control, and annunciation of water flow on each floor 
level.



Mike Stossel SET

<image002.png>

36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

[email protected] <mailto:[email protected]>



From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of 
Fpdcdesign
Sent: Tuesday, November 6, 2018 3:38 PM
To: Sprinklerforum <[email protected] 
<mailto:[email protected]> >
Subject: Back to back floor controls.



I am working on an existing two story plus attic wood frame building. The 
engineer is requiring zone control assemblies (butterfly valve plus riser 
manifold) for every level including the attic. I have designed it so there is a 
bull head tee at the top of a 4” riser with the assemblies on either side of 
the tee. Given that the flow switches are going to be in close proximity, 
should I install a check valve between the butterfly valve and the manifold?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to