Can someone clarify the verbiage of 8.3.2.5(2) (NFPA13 2013) in the 
Ordinary-Temp column for heads next to a diffuser ( c)? It says "Any distance 
except as shown under Intermediate-Temperature Rating Column". I have an AHJ 
saying that any head within 30" of a diffuser must be an 
Intermediate-Temperature head.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>