Brian,

There are much smarter people on here than me, but I have always understood 
that it means the Ordinary Temp heads are acceptable in any distance in 
relation to the Diffuser except the 1ft radius from the edge extending 1 in 
below to 2'-6" above for the downward discharge as noted in the table.  Similar 
for the Horizontal discharge per table 8.3.2.5(a).


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV    Dynamic Fire Designs

Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com/>


Dynamic Fire Designs • 247 Winthrop Dr. • Spring Hill • FL • 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.




________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Brian Harris <[email protected]>
Sent: Monday, November 19, 2018 2:32 PM
To: [email protected]
Subject: Heads Near Diffusers


Can someone clarify the verbiage of 8.3.2.5(2) (NFPA13 2013) in the 
Ordinary-Temp column for heads next to a diffuser ( c)? It says “Any distance 
except as shown under Intermediate-Temperature Rating Column”. I have an AHJ 
saying that any head within 30” of a diffuser must be an 
Intermediate-Temperature head.



Brian Harris, CET