...Yes,
just a couple of letters is all.   Wood construction is type V.  If you
have no fire-resistance protection on the wood meeting 1-hour ASMT E196
test, you have type V-B (IBC language).   I am not a NY PE, so I don't know
any recent reasons for the declaration, but the old reasons were:

a.  declaring construction type was about at ground zero of design.
b.  contruction type is used to define your maximum area and height of
building, along with other variables (occupancy type, setbacks,
sprinklers...)

You might want to take a couple hours and read the IBC chapters on
Construction Types and Fire Resistance Ratings.

Scot Deal
Excelsior Risk and Fire Safety Engineering
gms:  +420 606 872 129   (GMT + 1)




On Fri, Feb 22, 2019 at 8:44 PM Christopher Connor <[email protected]>
wrote:

> We have been requested by a general contractor to look into and possibly
> furnish signage required by NY state code that indicates the building
> construction type. They are wood construction townhomes which will contain
> some sort of truss-construction and OSB.
>
> I’m pretty sure if I have the correct requirements found here
> https://www.dos.ny.gov/dcea/pdf/Part1264.pdf but wanted to see if anyone
> on here had run into this whether in NY or elsewhere. What were those
> requirements?
>
> My understanding is the signs serve as a warning for fire departments of
> the dangers of the construction-type when in a fire situation.
>
> Are the signs required on dwelling units and townhomes? And is it really
> just a letter or two that designates the construction type?
>
> Thank you in advance for your input.
>
>
>
>
>
> *Christopher J. Connor*
>
> Design Engineer
>
> [image: Description: Description: Description: Email_Sig_Logo]
>
> *C:* 570.780.0732  ·  *W:* 877.324.ROWE  ·  *F:* 570.837.6335
>
> PO Box 407 · 7993 US Route 522, Suite 1 · Middleburg, PA 17842
>
> 505A Cornerstone Court · Hillsborough, NC 27278
>
> *RoweSprinkler.com  *·  [email protected]
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to