A main drain test out of a 2 inch main drain valve is not capable of
measuring the full capacity of the water supply on a municipal water
system, nor would it yield accurate results.    For example a significant
pressure drop on a 2 inch main drain test would indicate a possible closed
valve on the lead in piping from the supply main,  thus not truly measuring
the main capacity.   So agreeing with  Mr. Bilbo,  would never rely on a 2
inch main drain test for designing a fire sprinkler system.

On Mon, Mar 11, 2019 at 11:56 AM Skyler Bilbo <[email protected]>
wrote:

> I may do this sometimes, just to get an idea of the water supply, early on
> in a bid, but I would never rely on this for the design of a fire sprinkler
> system.  There are a lot of reasons for this.  If you do a quick internet
> search for "Water Measurement Using Two Inch Drain Tests", you will find a
> pretty awesome educational resource for this.  Make sure you read the whole
> thing.  Again, do not rely on a drain test.
>
>