Noted as subtext was use of direct read meter in lieu of standard pitot and 
calc’s.

https://www.mccrometer.com/asset-get.download.jsa?id=52003821668

We’ve used this. Standard gauge placed on adjacent hydrant. We were not using 
one meter of a 2” main drain. We were using up to four (4) on two different 
hydrants. We attempted to approach or exceed design flow. We wanted to be as 
far away from normal background flow as possible.

A primary goal vs pitot was not washing out existing business plantings. I’ve 
had a few sprinkler firms with a cavalier attitude about this damage. Unlike 
sprinkler companies fire marshal’s offices are subject to concerns, expressed 
through Mayor’s office, of existing community.

Best.

Bruce Verhei 

> On Mar 11, 2019, at 12:37, Matthew J Willis <[email protected]> wrote:
> 
> As others have stated, 2 separate animals.
> However, it is a measurable water flow at a certain pressure.
> It can be equated as available water.
> Keep in mind, the flow test should occur as close to the system demand as 
> possible.
> No extrapolation.
>  
> R/
> Matt
>  
> Matthew J. Willis, CWBSP
> Design Manager /3-D Specialist
> Rapid Fire Protection Inc.
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>  
> <image002.png>
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Kenan Bruce
> Sent: Monday, March 11, 2019 9:31 AM
> To: [email protected]
> Subject: Hydrant Flow vs Drain test
>  
> For additions to existing sprinkler systems, has anyone ever verified that a 
> 2” drain test is comparable to a hydrant flow test?
>  
> Thanks,
>  
>  
>  
> <image003.jpg>
> Kenan Bruce
>  
> Fire Technology, LLC
> 2005 Westside Drive
> Augusta, GA 30907
> T: 706-650-7730
> F: 706-650-7731
>  
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to