Do you mind providing a link to the specific article referenced?

On Mon, Mar 11, 2019 at 11:56 AM Skyler Bilbo <[email protected]>
wrote:

> I may do this sometimes, just to get an idea of the water supply, early on
> in a bid, but I would never rely on this for the design of a fire sprinkler
> system.  There are a lot of reasons for this.  If you do a quick internet
> search for "Water Measurement Using Two Inch Drain Tests", you will find a
> pretty awesome educational resource for this.  Make sure you read the whole
> thing.  Again, do not rely on a drain test.
>
>
> -Skyler
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to