The NFPA 13 committee believes the tank size is indeed based on the CALCULATED 
volume of water.  I know this because I attempted several cycles ago to state 
we should simply use the curves with a modifier.  I was almost burned at the 
stake for uttering such blasphemy. 

Roland


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Mar 20, 2019, at 7:48 AM, AKS-Gmail-IMAP <[email protected]> wrote:
> 
> Tank sizing for some situations presents an uncomfortable dilemma because 
> there are pressures from all sides to minimize the tank size yet we all know 
> the tank contains the single most important item. Some codes can be argued to 
> say the size is for sprinkler demand only. The code might also qualify that 
> by implying the actual system calculated sprinkler demand is used for sizing. 
> So in this case the OH-2 system might have a 1.8 overage at its most 
> demanding location. But then what happens if the fire event occurs at the 
> least pressure demanding part of the system where the overage is higher than 
> 1.8? Here we can only hope that more water in less time is better and perhaps 
> not so many sprinklers open and someone is present to manage the run time. 
> The same pressures to limit the tank size might also work against installing 
> a more water efficient sprinkler system for that OH-2 space. 
> 