I think you do, unless somehow your EC heads meet that spacing criteria (which 
would be a horribly inefficient use of EC sprinklers). But I'm hoping someone 
will disagree with me and have a good answer as to why you don't.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Tuesday, May 7, 2019 9:34 AM
To: [email protected]
Subject: [EXTERNAL] EC Heads and open Grid Ceilings

We have an existing building that has extended coverage heads installed, the 
tenant improvement involves floating wood grated ceilings that are more than 
70% open and will be about 18" below the sprinkler head. Light hazard occupancy.

NFPA #13 (2013) section 8.15.14 Open Grid Ceilings does not make mention of EC 
heads.

Do we need to change all the heads in this area to standard coverage heads?



Thank you