If you have 18" clear from deflector down to top-of-grating, I would think
the grating members could be up to 4' wide.

 

Ed K

Bamford Fire

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mike Stossel
Sent: Tuesday, May 07, 2019 12:45 PM
To: [email protected]
Subject: RE: [EXTERNAL] EC Heads and open Grid Ceilings

 

I could be completely off base with this, but does your ceiling need to
follow open grid ceilings?  The thought crossing my mind is a 2"x4" hung on
its edge spaced a couple feet apart or more of a ceiling grid system
installed without the tiles.  Would the three times rule apply instead of
the open grid rules?

 

Mike Stossel SET



36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

 <mailto:[email protected]> [email protected]

 

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > On Behalf Of
Kyle.Montgomery
Sent: Tuesday, May 7, 2019 1:17 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: [EXTERNAL] EC Heads and open Grid Ceilings

 

I think you do, unless somehow your EC heads meet that spacing criteria
(which would be a horribly inefficient use of EC sprinklers). But I'm hoping
someone will disagree with me and have a good answer as to why you don't.

 

-Kyle M

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of James Crawford
Sent: Tuesday, May 7, 2019 9:34 AM
To: [email protected]
<mailto:[email protected]> 
Subject: [EXTERNAL] EC Heads and open Grid Ceilings

 

We have an existing building that has extended coverage heads installed, the
tenant improvement involves floating wood grated ceilings that are more than
70% open and will be about 18" below the sprinkler head. Light hazard
occupancy.

 

NFPA #13 (2013) section 8.15.14 Open Grid Ceilings does not make mention of
EC heads.

 

Do we need to change all the heads in this area to standard coverage heads?

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected] <mailto:[email protected]> 

Web www.phaserfire.ca <http://www.phaserfire.ca> 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to