Nope, the omission of sprinklers by any means or allowances null and voids the “sprinklered throughout” classification. That is addressed within the IBC Commentary. Just had this discussion on a project myself.
It is the same if you substitute a clean agent for sprinklers in an area. No longer considered sprinklered throughout. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | [email protected]<mailto:[email protected]> | www.jacobs.com<http://www.jacobs.com/> 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected]> On Behalf Of James Litvak via Sprinklerforum Sent: Thursday, October 24, 2019 12:18 PM To: [email protected] Cc: James Litvak <[email protected]> Subject: [EXTERNAL] Trying to determine hydrant locations per IFC, wondering how sprinkler coverage omissions will affect distances. I'm working on a manufacturing facility that is building type IIB. Per the fire-flow requirement of 8,000 gpm, the average spacing of hydrants will need to be 200 feet, per IFC Table C102.1. However, note f will allow a 50-percent spacing increase if "the building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 of the International Fire Code" (emphasis mine). The reason I bolded throughout is because approximately 2/3 of the building has sprinklers omitted in accordance with exceptions from Section 903.3.1.1. So my question is, if Section 903.3.1.1 is being followed such that it is being applied throughout the building, and the areas of the building that aren't being sprinklered are allowed by that section, does this count as "equipped throughout"? ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org