Nope, the omission of sprinklers by any means or allowances null and voids the 
“sprinklered throughout” classification.  That is addressed within the IBC 
Commentary.  Just had this discussion on a project myself.

It is the same if you substitute a clean agent for sprinklers in an area.  No 
longer considered sprinklered throughout.



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of James Litvak via Sprinklerforum
Sent: Thursday, October 24, 2019 12:18 PM
To: [email protected]
Cc: James Litvak <[email protected]>
Subject: [EXTERNAL] Trying to determine hydrant locations per IFC, wondering 
how sprinkler coverage omissions will affect distances.

I'm working on a manufacturing facility that is building type IIB. Per the 
fire-flow requirement of 8,000 gpm, the average spacing of hydrants will need 
to be 200 feet, per IFC Table C102.1. However, note f will allow a 50-percent 
spacing increase if "the building is equipped throughout with an automatic 
sprinkler system in accordance with Section 903.3.1.1 of the International Fire 
Code" (emphasis mine). The reason I bolded throughout is because approximately 
2/3 of the building has sprinklers omitted in accordance with exceptions from 
Section 903.3.1.1. So my question is, if Section 903.3.1.1 is being followed 
such that it is being applied throughout the building, and the areas of the 
building that aren't being sprinklered are allowed by that section, does this 
count as "equipped throughout"?

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to