I’ve also wrestled with this before but I don’t have the IBC commentary Craig 
mentions in my notes, but see the following references…

IFC 2012
903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code require 
that a building or portion thereof be equipped throughout with an automatic 
sprinkler system in accordance with this section, sprinklers shall be installed 
throughout in accordance with NFPA 13 except as provided in Section 903.3.1.1.1.


NFPA 13, 2013 ed.

Chapter 8 Installation Requirements

8.1* Basic Requirements.

8.1.1* The requirements for spacing, location, and position of sprinklers shall 
be based on the following principles:

(1) Sprinklers shall be installed throughout the premises.

(2) Sprinklers shall be located so as not to exceed the maximum protection area 
per sprinkler.

(3)*Sprinklers shall be positioned and located so as to provide satisfactory 
performance with respect to activation time and distribution.

(4) Sprinklers shall be permitted to be omitted from areas specifically allowed 
by this standard.

(5) When sprinklers are specifically tested and test results demonstrate that 
deviations from clearance requirements to structural members do not impair the 
ability of the sprinkler to control or suppress a fire, their positioning and 
locating in accordance with the test results shall be permitted.

(6) Clearance between sprinklers and ceilings exceeding the maximums specified 
in this standard shall be permitted, provided that tests or calculations 
demonstrate comparable sensitivity and performance of the sprinklers to those 
installed in conformance with these sections.

(7) Furniture, such as portable wardrobe units, cabinets, trophy cases, and 
similar features not intended for occupancy, does not require sprinklers to be 
installed in them. This type of feature shall be permitted to be attached to 
the finished structure.

(8)*Sprinklers shall not be required to be installed within electrical 
equipment, mechanical equipment, or air handling units not intended for 
occupancy.

A.8.1.1
This standard contemplates full sprinkler protection for all areas including 
walk-in coolers, freezers, bank vaults, and similar areas. Other NFPA standards 
that mandate sprinkler installation might not require sprinklers in certain 
areas. Based upon experience and testing, sprinklers have been found to be 
effective and necessary at heights in excess of 50 ft. For a building to meet 
the intended level of protection afforded by NFPA 13, sprinklers must not be 
omitted from such high ceiling spaces. The requirements of this standard should 
be used insofar as they are applicable. The authority having jurisdiction 
should be consulted in each case. A building is considered sprinklered 
throughout when protected in accordance with the requirements of this standard.




Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, 
ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum <[email protected]> On Behalf 
Of James Litvak via Sprinklerforum
Sent: Thursday, October 24, 2019 12:14 PM
To: Prahl, Craig/GVL <[email protected]>
Cc: James Litvak <[email protected]>; [email protected]
Subject: Re: [EXTERNAL] Trying to determine hydrant locations per IFC, 
wondering how sprinkler coverage omissions will affect distances.

Interesting. I don't have access to a copy of the Code and Commentary. Would 
you be able to copy/paste the relevant section, or tell me where to find it? I 
will try to get access to it.
Thanks.

On Thu, Oct 24, 2019 at 12:35 PM Prahl, Craig/GVL 
<[email protected]<mailto:[email protected]>> wrote:
Nope, the omission of sprinklers by any means or allowances null and voids the 
“sprinklered throughout” classification.  That is addressed within the IBC 
Commentary.  Just had this discussion on a project myself.

It is the same if you substitute a clean agent for sprinklers in an area.  No 
longer considered sprinklered throughout.



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of James Litvak via Sprinklerforum
Sent: Thursday, October 24, 2019 12:18 PM
To: 
[email protected]<mailto:[email protected]>
Cc: James Litvak <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] Trying to determine hydrant locations per IFC, wondering 
how sprinkler coverage omissions will affect distances.

I'm working on a manufacturing facility that is building type IIB. Per the 
fire-flow requirement of 8,000 gpm, the average spacing of hydrants will need 
to be 200 feet, per IFC Table C102.1. However, note f will allow a 50-percent 
spacing increase if "the building is equipped throughout with an automatic 
sprinkler system in accordance with Section 903.3.1.1 of the International Fire 
Code" (emphasis mine). The reason I bolded throughout is because approximately 
2/3 of the building has sprinklers omitted in accordance with exceptions from 
Section 903.3.1.1. So my question is, if Section 903.3.1.1 is being followed 
such that it is being applied throughout the building, and the areas of the 
building that aren't being sprinklered are allowed by that section, does this 
count as "equipped throughout"?

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

______________________________________________________________________
This email originated from an external source and has been scanned by the 
Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to