Bob, The committee wants to see relative elevation changes. This helps with lengths of pipe and calcs too. We use the word relative because it doesn't need to be Above Sea Level. (But I think you already know this!!)
Cecil It should be recognized that the above is my opinion as a member of the NFPA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the the NFPA, nor any of their technical committees. Sincerely, Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 217.607.0325 www.sprinkleracademy.com [email protected] ?? OUR STUDENTS SAVE LIVES!! ________________________________ From: Sprinklerforum <[email protected]> on behalf of Bob Knight via Sprinklerforum <[email protected]> Sent: Thursday, January 9, 2020 3:41:36 PM To: [email protected] <[email protected]> Cc: Bob Knight <[email protected]> Subject: NFPA 13, 23.1.3 (37) >From NFPA 13 (2013 ED), 23.1.3 (37) Relative elevations of sprinklers, >junction points, and supply or reference points. This is probably an obvious question, but not to me. What is this asking for? Thank you, Bob Knight, CET III Fire by Knight, LLC 208-318-3057 [FBK-LOGO-EMAIL]