Ken,

Isn't it the information already provided for in the hydraulic calculations?
I'm only asking because there is an AHJ that has asked for an isometric
drawing be provided on the plans showing "the relative elevations of
sprinklers, junction points, and supply or reference points. See NFPA
13-2013 Section 23.1.3 (37)".

There is no isometric requirement in NFPA 13 that I'm aware of.  It seems
like this is the information in the calculations that would correspond to
the hydraulic node points on the drawing.

 

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Parsley Consulting via Sprinklerforum
Sent: Thursday, January 09, 2020 4:02 PM
To: Bob Knight via Sprinklerforum
Cc: Parsley Consulting
Subject: private reply

 

Bob,

My thought is that it's asking for a way to evaluate the one variable which
can't be changed - elevation gain or loss.

Just my opinion,

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website <http://www.parsleyconsulting.com/>  

On 01/09/2020 1:41 PM, Bob Knight via Sprinklerforum wrote:

>From NFPA 13 (2013 ED), 23.1.3 (37)  Relative  elevations  of  sprinklers,
junction  points,  and supply or reference points.

This is probably an obvious question, but not to me.  What is this asking
for?

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

FBK-LOGO-EMAIL

 





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to