I have a little experience with this.  I have seen a system brand called
"Flamex" on the dust collection ducts.  This system uses flame sensors and
solenoids to extinguish a fire in the duct, which is a better system than
just installing sprinklers in there.  I can say that installing sprinklers
in the top of the filter units is a good idea.  I have seen fires in these
at a couple of facilities, and the employees on one of the sites later
admitted "it was a whole lot cheaper to buy the filters that aren't flame
resistant, like the manufacturer recommends..."  The Flamex people can be
helpful if you give them a call (it is what they do).  Be very careful
about your liability with these systems (speaking of which, this email is
by no means a substitute for an engineered fire protection system), and it
is important to mention these usually have a high explosion (read:
deflagration) risk, which needs to be addressed.  Also, you might consider
some kind of physical protection for any heads you install.  I hope this
was helpful, because I know how I felt when I first started going through
these systems.


- Skyler

On Mon, Feb 24, 2020 at 9:46 AM Dewayne Martinez via Sprinklerforum <
[email protected]> wrote:

> I am trying to figure out the proper design criteria for a combustible
> dust collector and associated duct work.
>
>
>
> NFPA 654-2020ed section 9.3.5.2
>
> NFPA 652-2019ed section 9.8.5.3
>
> Both refer you back to NFPA 13
>
>
>
> There is no section on NFPA 13-2013 for dust collectors.  The closest I
> can find is section 22.4 – spray applications using flammable or
> combustible materials.
>
> Anyone else have experience with this?
>
> Thanks,
>
>
>
> Dewayne Martinez
>
> Fire Protection Design Manager
>
>
>
> *TOTAL* *Mechanical*
>
> *Building* *Integrity*
>
>
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
>
> [email protected]
>
> Ph:  262-522-7110
>
> Cell: 414-406-5208
>
> http://www.total-mechanical.com/
>
>
>
> [image: cid:[email protected]]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to