Flamex has been around for several decades, I believe under a couple different 
corporate ownerships. It is not a new technology.

I’m more used to seeing as part of an overall dust explosion control system. 
Usually I’ve worked with a mechanical engineer whose specialty is dust 
explosion control.

Most common is the pair of spark detection, spark suppression, then downstream 
again, spark detection. Second detection series releases abort gate.

Current retroactive standards for dust systems are going into effect. Expect 
more discussion. 

.....

Stay back from abort gates. Anything that you need to reset with a come along, 
and trips too fast for eye to see is hazardous in its own right. 

Best.

Bruce Verhei 


> On Feb 24, 2020, at 08:03, Skyler Bilbo via Sprinklerforum 
> <[email protected]> wrote:
> 
> I have a little experience with this.  I have seen a system brand called 
> "Flamex" on the dust collection ducts.  This system uses flame sensors and 
> solenoids to extinguish a fire in the duct, which is a better system than 
> just installing sprinklers in there.  I can say that installing sprinklers in 
> the top of the filter units is a good idea.  I have seen fires in these at a 
> couple of facilities, and the employees on one of the sites later admitted 
> "it was a whole lot cheaper to buy the filters that aren't flame resistant, 
> like the manufacturer recommends..."  The Flamex people can be helpful if you 
> give them a call (it is what they do).  Be very careful about your liability 
> with these systems (speaking of which, this email is by no means a substitute 
> for an engineered fire protection system), and it is important to mention 
> these usually have a high explosion (read: deflagration) risk, which needs to 
> be addressed.  Also, you might consider some kind of physical protection for 
> any heads you install.  I hope this was helpful, because I know how I felt 
> when I first started going through these systems.
> 
> 
> - Skyler
> 
>> On Mon, Feb 24, 2020 at 9:46 AM Dewayne Martinez via Sprinklerforum 
>> <[email protected]> wrote:
>> I am trying to figure out the proper design criteria for a combustible dust 
>> collector and associated duct work.
>> 
>>  
>> 
>> NFPA 654-2020ed section 9.3.5.2
>> 
>> NFPA 652-2019ed section 9.8.5.3
>> 
>> Both refer you back to NFPA 13
>> 
>>  
>> 
>> There is no section on NFPA 13-2013 for dust collectors.  The closest I can 
>> find is section 22.4 – spray applications using flammable or combustible 
>> materials.
>> 
>> Anyone else have experience with this?
>> 
>> Thanks,
>> 
>>  
>> 
>> Dewayne Martinez
>> 
>> Fire Protection Design Manager
>> 
>>  
>> 
>> TOTAL Mechanical
>> 
>> Building Integrity
>> 
>> 
>> W234 N2830 Paul Rd.
>> Pewaukee, WI  53072
>> 
>> [email protected]
>> 
>> Ph:  262-522-7110
>> 
>> Cell: 414-406-5208
>> 
>> http://www.total-mechanical.com/ 
>> 
>>           
>> 
>> <image001.png>
>> 
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to