> I have a little experience with this.  I have seen a system brand called 
> "Flamex" on the dust collection ducts.  This system uses flame sensors and 
> solenoids to extinguish a fire in the duct, which is a better system than 
> just installing sprinklers in there.  I can say that installing sprinklers in 
> the top of the filter units is a good idea.  I have seen fires in these at a 
> couple of facilities, and the employees on one of the sites later admitted 
> "it was a whole lot cheaper to buy the filters that aren't flame resistant, 
> like the manufacturer recommends..."  The Flamex people can be helpful if you 
> give them a call (it is what they do).  Be very careful about your liability 
> with these systems (speaking of which, this email is by no means a substitute 
> for an engineered fire protection system), and it is important to mention 
> these usually have a high explosion (read: deflagration) risk, which needs to 
> be addressed.  Also, you might consider some kind of physical protection for 
> any heads you install.  I hope this was helpful, because I know how I felt 
> when I first started going through these systems.
> 
> 
> - Skyler
> 
>> On Mon, Feb 24, 2020 at 9:46 AM Dewayne Martinez via Sprinklerforum 
>> <[email protected]> wrote:
>> I am trying to figure out the proper design criteria for a combustible dust 
>> collector and associated duct work.
>> 
>>  
>> 
>> NFPA 654-2020ed section 9.3.5.2
>> 
>> NFPA 652-2019ed section 9.8.5.3
>> 
>> Both refer you back to NFPA 13
>> 
>>  
>> 
>> There is no section on NFPA 13-2013 for dust collectors.  The closest I can 
>> find is section 22.4 – spray applications using flammable or combustible 
>> materials.
>> 
>> Anyone else have experience with this?
>> 
>> Thanks,
>> 
>>  
>> 
>> Dewayne Martinez
>> 
>> Fire Protection Design Manager
>> 
>>  
>> 
>> TOTAL Mechanical
>> 
>> Building Integrity
>> 
>> 
>> W234 N2830 Paul Rd.
>> Pewaukee, WI  53072
>> 
>> [email protected]
>> 
>> Ph:  262-522-7110
>> 
>> Cell: 414-406-5208
>> 
>> http://www.total-mechanical.com/ 
>> 
>>           
>> 
>> <image001.png>
>> 
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to