In my opinion, only the sprinkler(s) protecting the balcony in question
needs to be calculated.  13R is quiet on this subject, but if you look at

*7.2.5 The number of design sprinklers for a corridor or breezeway outside
the dwelling unit shall include up to the four most hydraulically demanding
adjacent sprinklers. *
I would consider a corridor or breezeway a much more challenging fire that
affects the life safety of the occupants more than a balcony.  As long as
the multiply balconies are not attached to each other, the gap will allow
the heat to be vented to atmosphere.

John


John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Grow your business with ITM.*

Professionalize the role of your inspection team with AFSA’s comprehensive
20-month ITM Inspector Development program that provides a blended learning
environment teamed with robust curriculum created by top industry leaders. Now
enrolling <https://www.firesprinkler.org/itm> for Spring 2020.


On Mon, Mar 9, 2020 at 10:31 AM Travis Mack via Sprinklerforum <
[email protected]> wrote:

> What edition are you using? It is in the standard from 2013 and newer I
> believe.
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> 480-505-9271 x700
> MFP Design, LLC
> www.mfpdesign,com
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
>
> On Mar 9, 2020, at 8:27 AM, J H via Sprinklerforum <
> [email protected]> wrote:
>
> 
> I don't doubt their efficacy or necessity - my question is essentially how
> do you calculate an area that is not required to be sprinklered by the
> standard in the first place and does not meet w/ the definition of a
> compartment? I'll just go ahead and do a four head calc for this balcony
> like I always do but I was wondering what others were doing. My second
> thought would be to just size the piping to the balcony sprinklers using
> the same interior pipe sizes without calculating it as it's own
> compartment. We've had similar situations arise when jurisdictions required
> limited attic protection in 13D systems and didn't give any guidance on how
> to calculate the required quick response sprinklers they were requiring at
> the ridge.
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>  Virus-free.
> www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
> <#m_7710434825962946091_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> On Fri, Mar 6, 2020 at 4:33 PM Bruce Verhei via Sprinklerforum <
> [email protected]> wrote:
>
>>
>>
>> https://www-dailyherald-com.cdn.ampproject.org/c/s/www.dailyherald.com/amp-article/20200221/news/200229736/
>>
>> Balcony fire, spk head.
>>
>> On Mar 6, 2020, at 13:11, Pete Schwab via Sprinklerforum <
>> [email protected]> wrote:
>>
>> We only calculate the single balcony in question.
>>
>>
>>
>>
>>
>> Peter Schwab
>>
>> VP of Purchasing and Engineering technologies
>>
>>
>>
>> Wayne Automatic Fire Sprinklers Inc.
>>
>> 222 Capitol Court
>>
>> Ocoee, Fl 34761
>>
>>
>>
>> *Mobile: (407) 468-8248*
>>
>> Direct: (407) 877-5570
>>
>> Fax: (407) 656-8026
>>
>>
>>
>> www.waynefire.com
>>
>>
>>
>> <image001.jpg>
>>
>>
>>
>> <image002.png>
>>
>>
>>
>> *I sleep in a sprinklered home, do you? *
>>
>>
>>
>>
>>
>> *From:* Sprinklerforum <[email protected]> *On
>> Behalf Of *J H via Sprinklerforum
>> *Sent:* Friday, March 6, 2020 3:52 PM
>> *To:* [email protected]
>> *Cc:* J H <[email protected]>
>> *Subject:* How are you guys handling calcs for 13R balconies?
>>
>>
>>
>> I was wondering how you guys are handling calculations for 13R balconies
>> since the sprinklers aren't even required per 13R but are mandated by the
>> IBC? Treating it as a compartment in this case means I have to do a 4 head
>> calc when the rest of the project only requires 2 heads calculated due to
>> compartmentalization. It's not a big deal but kind of a bummer when you can
>> have really small pipe sizes for a project if it weren't for those pesky
>> guys on the balcony!
>>
>>
>>
>> J
>>
>>
>>
>>
>>
>>
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>>
>> Virus-free. www.avast.com
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to