John, so that's pretty much the reason I asked this question; there's no
compartment but I do have 4 contiguous sprinklers that are open to the
elements. If this were a '13 system I think it would be cut and dry since
the compartment requirement goes away - being a 13R system it's a bit of a
gray area, however, I just calc all four of them and call it a day but it
kind of sucks when you're forced to increase a lot of main from 1 1/4" to 1
1/2" in a building w/ little room for install, consisting of TJI
construction and ceilings being installed tight to the underside of them.

<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Tue, Mar 10, 2020 at 7:48 AM John Denhardt via Sprinklerforum <
[email protected]> wrote:

> That's my point.  Calculated the sprinklers that are on any single
> balcony.  If the balconies are continuous, keep adding sprinklers to a
> maximum of 4 sprinklers.  However, if there are separations between the
> balconies, do not extend just to reach 4 sprinklers.
>
> The issue i have is the typical balcony is not considered a compartment as
> no walls exists.  So, in accordance with NFPA 13R, where is the compartment?
>
> Thanks.
> John
> John August Denhardt, PE
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
> m: p: 301-343-1457
> 214-349-5965 ext 121
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Grow your business with ITM.*
>
> Professionalize the role of your inspection team with AFSA’s comprehensive
> 20-month ITM Inspector Development program that provides a blended learning
> environment teamed with robust curriculum created by top industry leaders. Now
> enrolling <https://www.firesprinkler.org/itm> for Spring 2020.
>
>
> On Tue, Mar 10, 2020 at 4:31 AM Fpdcdesign via Sprinklerforum <
> [email protected]> wrote:
>
>> First, even if it is not required by the standard, you would calculate it
>> as if it was.
>>
>> Second, is the design such that a single balcony requires 4 or more
>> sprinklers?
>>
>>
>> On Mar 10, 2020 at 12:23 AM, <J H via Sprinklerforum
>> <[email protected]>> wrote:
>>
>> I don't doubt their efficacy or necessity - my question is essentially
>> how do you calculate an area that is not required to be sprinklered by the
>> standard in the first place and does not meet w/ the definition of a
>> compartment? I'll just go ahead and do a four head calc for this balcony
>> like I always do but I was wondering what others were doing. My second
>> thought would be to just size the piping to the balcony sprinklers using
>> the same interior pipe sizes without calculating it as it's own
>> compartment. We've had similar situations arise when jurisdictions required
>> limited attic protection in 13D systems and didn't give any guidance on how
>> to calculate the required quick response sprinklers they were requiring at
>> the ridge.
>>
>>
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>>  Virus-free.
>> www.avast.com
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
>> <#m_2146389310944593343_m_-6760020793219401511_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>>
>> On Fri, Mar 6, 2020 at 4:33 PM Bruce Verhei via Sprinklerforum <
>> [email protected]> wrote:
>>
>>>
>>>
>>> https://www-dailyherald-com.cdn.ampproject.org/c/s/www.dailyherald.com/amp-article/20200221/news/200229736/
>>>
>>> Balcony fire, spk head.
>>>
>>> On Mar 6, 2020, at 13:11, Pete Schwab via Sprinklerforum <
>>> [email protected]> wrote:
>>>
>>> We only calculate the single balcony in question.
>>>
>>>
>>>
>>>
>>>
>>> Peter Schwab
>>>
>>> VP of Purchasing and Engineering technologies
>>>
>>>
>>>
>>> Wayne Automatic Fire Sprinklers Inc.
>>>
>>> 222 Capitol Court
>>>
>>> Ocoee, Fl 34761
>>>
>>>
>>>
>>> *Mobile: (407) 468-8248*
>>>
>>> Direct: (407) 877-5570
>>>
>>> Fax: (407) 656-8026
>>>
>>>
>>>
>>> www.waynefire.com
>>>
>>>
>>>
>>> <image001.jpg>
>>>
>>>
>>>
>>> <image002.png>
>>>
>>>
>>>
>>> *I sleep in a sprinklered home, do you? *
>>>
>>>
>>>
>>>
>>>
>>> *From:* Sprinklerforum <[email protected]> *On
>>> Behalf Of *J H via Sprinklerforum
>>> *Sent:* Friday, March 6, 2020 3:52 PM
>>> *To:* [email protected]
>>> *Cc:* J H <[email protected]>
>>> *Subject:* How are you guys handling calcs for 13R balconies?
>>>
>>>
>>>
>>> I was wondering how you guys are handling calculations for 13R balconies
>>> since the sprinklers aren't even required per 13R but are mandated by the
>>> IBC? Treating it as a compartment in this case means I have to do a 4 head
>>> calc when the rest of the project only requires 2 heads calculated due to
>>> compartmentalization. It's not a big deal but kind of a bummer when you can
>>> have really small pipe sizes for a project if it weren't for those pesky
>>> guys on the balcony!
>>>
>>>
>>>
>>> J
>>>
>>>
>>>
>>>
>>>
>>>
>>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>>>
>>> Virus-free. www.avast.com
>>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>> _______________________________________________ Sprinklerforum mailing
>> list [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to