Ask him to show you the requirement for that...Chapter and verse. The AHJ can' 
just make rules up as he decides he needs to. I know of no reason to leave them 
in place unless they become totally in accessable. The only thing I can imagine 
that would create that condition would be a hard ceiling.Good luck.Sent from my 
Sprint Samsung Galaxy S8.
-------- Original message --------From: John Irwin via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org> Date: 6/18/20  2:21 PM  (GMT-05:00) 
To: sprinklerforum@lists.firesprinkler.org Cc: John Irwin 
<jir...@quickresponsefl.com> Subject: Uprights in non combustible concealed 
space 

We installed temporary upright Protection in a partially occupied building 
during a major renovation. We then came back and dropped pendent heads in the 
new ceiling. We left the uprights above the new ceiling. Fire inspector says we 
need to remove the uprights
 now. Is there a basis for removing these? I realize they are not required but 
are they permitted to remain? 



John Irwin