I could be wrong, but isn’t there something in IFC that states a fire 
protection system left in place needs to be compliant for the area?  I’ve had 
inspectors interpret as you indicate.  It’s the rationale that you can’t leave 
dead sprinkler pipe in the air.

 

Now, I have had this same situation and argued in the case the sprinkler was 
just a “glorified plug.”  Contractor was in a bind, no access to remove the 
sprinklers.  

 

But, if you dig into the fire code, you may find where he is at least starting 
from.  You won’t find your answer in NFPA 13.

 

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

Engineering Manager

MFP Design

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

NEW MOBILE: 480-272-2471

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

 <mailto:travis.m...@ferguson.com> travis.m...@ferguson.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?

*If you do not already have an account with ferguson.com, click  
<https://www.ferguson.com/account-registration> here to register.*

**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features.  
<http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003>
 Apple iOS devices or  
<http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003>
 Android devices**

 

 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Ed Vining via Sprinklerforum
Sent: Thursday, June 18, 2020 11:35 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ed Vining <fpe...@gmail.com>
Subject: Re: Uprights in non combustible concealed space

 

Not really. The codes and standards determine the decision.

 

This may be my last post. At the age of 95 I am starting to lose interest.

 

 

Ed Vining

2770 Pleasant Hill Rd Apt 228

Pleasant Hill CA 95423

925-448-2159                                 

fpe...@gmail.com <mailto:fpe...@gmail.com> 

 

 

On Thu, Jun 18, 2020 at 11:28 AM Cary Webber via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> > wrote:

On the downside, if all areas above the ceilings are not protected, it may give 
a false sense of security. On the upside, more sprinklers are better, and even 
if not required they can act as detectors in the space. Bottom line is that the 
AHJ has ultimate decision making authority.

 

 

 

Cary Webber CFPS Director, Technical Services

Reliable Automatic Sprinkler Co., Inc.

1470 Smith Grove Road, Liberty, SC  29657 

Tel: 864-843-5161 

 

 <http://www.reliablesprinkler.com/> 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of John 
Irwin via Sprinklerforum
Sent: Thursday, June 18, 2020 2:21 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: John Irwin <jir...@quickresponsefl.com <mailto:jir...@quickresponsefl.com> >
Subject: Uprights in non combustible concealed space 

 

CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you can confirm the sender and know the 
content is safe. 

 

We installed temporary upright Protection in a partially occupied building 
during a major renovation. We then came back and dropped pendent heads in the 
new ceiling. We left the uprights above the new ceiling. Fire inspector says we 
need to remove the uprights now. Is there a basis for removing these? I realize 
they are not required but are they permitted to remain? 

 

John Irwin

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Uprights in non co... John Irwin via Sprinklerforum
    • RE: Uprights ... Cary Webber via Sprinklerforum
      • Re: Uprig... Ed Vining via Sprinklerforum
        • RE: U... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
          • R... Tony Silva via Sprinklerforum
            • ... Kyle.Montgomery via Sprinklerforum
        • RE: U... Steve Leyton via Sprinklerforum
          • R... Fpdcdesign via Sprinklerforum
        • RE: U... Reed A. Roisum, SET via Sprinklerforum
        • Re: U... Ben Young via Sprinklerforum
      • RE: Uprig... Anthony via Sprinklerforum
        • RE: U... Steve Leyton via Sprinklerforum
          • R... Anthony via Sprinklerforum
            • ... Steve Leyton via Sprinklerforum

Reply via email to