Yes, it is specified in NFPA 13. NFPA 13, does not tell you which buildings
are required to be sprinklered, which task is up to the building code or
local ordinances. However, if the building is sprinklered (whether by
mandate or voluntarily), it has to comply with NFPA 13. Note that the scope
of NFPA 13 is to provide minimum requirements for the design and
installation of automatic sprinkler systems. Not just the requirements for
systems that are mandated.

Just take the garage in your home. Depending on local requirements, you may
not require one for your house. However, if you build one, it has to comply
with code requirements.

So if you leave the sprinklers in the concealed space, make sure they
comply with code requirements.

My two cents, Tony

On Thu, Jun 18, 2020 at 12:48 PM Travis Mack, SET, CFPS, CWBSP, RME-G via
Sprinklerforum <sprinklerforum@lists.firesprinkler.org> wrote:

> *I could be wrong, but isn’t there something in IFC that states a fire
> protection system left in place needs to be compliant for the area?  I’ve
> had inspectors interpret as you indicate.  It’s the rationale that you
> can’t leave dead sprinkler pipe in the air.*
>
>
>
> *Now, I have had this same situation and argued in the case the sprinkler
> was just a “glorified plug.”  Contractor was in a bind, no access to remove
> the sprinklers.  *
>
>
>
> *But, if you dig into the fire code, you may find where he is at least
> starting from.  You won’t find your answer in NFPA 13.*
>
>
>
>
>
> [image: MFP_logo_F] <http://www.mfpdesign.com/>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> Engineering Manager
>
> MFP Design
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> NEW EXTENSION: 480-505-9271 ext. 700
>
> NEW MOBILE: 480-272-2471
>
> tm...@mfpdesign.com
>
> travis.m...@ferguson.com
>
> www.mfpdesign.com
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
>
>
> *Need/Want a faster way to check material pricing?  Build a material
> quote?  Check availability ?   Searching for an invoice?*
>
> *If you do not already have an account with ferguson.com, click *here*
> <https://www.ferguson.com/account-registration> to register.*
>
> **Have a Ferguson account? Download the Ferguson app for on-the-go access
> to your favorite ferguson.com features. *Apple iOS devices*
> <http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003>
>  or *Android devices*
> <http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003>
> **
>
>
>
>
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Ed Vining via Sprinklerforum
> *Sent:* Thursday, June 18, 2020 11:35 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* Ed Vining <fpe...@gmail.com>
> *Subject:* Re: Uprights in non combustible concealed space
>
>
>
> Not really. The codes and standards determine the decision.
>
>
>
> This may be my last post. At the age of 95 I am starting to lose interest.
>
>
>
>
>
> Ed Vining
>
> 2770 Pleasant Hill Rd Apt 228
>
> Pleasant Hill CA 95423
>
> 925-448-2159
>
> fpe...@gmail.com
>
>
>
>
>
> On Thu, Jun 18, 2020 at 11:28 AM Cary Webber via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org> wrote:
>
> On the downside, if all areas above the ceilings are not protected, it may
> give a false sense of security. On the upside, more sprinklers are better,
> and even if not required they can act as detectors in the space. Bottom
> line is that the AHJ has ultimate decision making authority.
>
>
>
>
>
>
>
> *Cary Webber CFPS* *Director, Technical Services*
>
> Reliable Automatic Sprinkler Co., Inc.
>
> 1470 Smith Grove Road, Liberty, SC  29657
>
> Tel: 864-843-5161
>
>
>
> [image: Image removed by sender.] <http://www.reliablesprinkler.com/>
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *John Irwin via Sprinklerforum
> *Sent:* Thursday, June 18, 2020 2:21 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* John Irwin <jir...@quickresponsefl.com>
> *Subject:* Uprights in non combustible concealed space
>
>
>
> *CAUTION:* This email originated from outside of the organization. Do not
> click links or open attachments unless you can confirm the sender and know
> the content is safe.
>
>
>
> We installed temporary upright Protection in a partially occupied building
> during a major renovation. We then came back and dropped pendent heads in
> the new ceiling. We left the uprights above the new ceiling. Fire inspector
> says we need to remove the uprights now. Is there a basis for removing
> these? I realize they are not required but are they permitted to remain?
>
>
>
> John Irwin
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Uprights in non co... John Irwin via Sprinklerforum
    • RE: Uprights ... Cary Webber via Sprinklerforum
      • Re: Uprig... Ed Vining via Sprinklerforum
        • RE: U... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
          • R... Tony Silva via Sprinklerforum
            • ... Kyle.Montgomery via Sprinklerforum
        • RE: U... Steve Leyton via Sprinklerforum
          • R... Fpdcdesign via Sprinklerforum
        • RE: U... Reed A. Roisum, SET via Sprinklerforum
        • Re: U... Ben Young via Sprinklerforum
      • RE: Uprig... Anthony via Sprinklerforum
        • RE: U... Steve Leyton via Sprinklerforum
          • R... Anthony via Sprinklerforum
            • ... Steve Leyton via Sprinklerforum
              • ... Dewayne Martinez via Sprinklerforum

Reply via email to