The 2018 International Building Code (IBC) has a section, 505.3.2, for 
automatic sprinkler coverage of equipment platforms.
The definition provided in the IBC for "equipment platform" is not limited to 
only "fuel fired" equipment.
I suspect the IBC section is here because of the tendency for out of view flat 
surfaces near equipment to accumulate filters and other "stuff" needed for the 
maintenance of the equipment.

SJ

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Sprinkler Academy - C Bilbo via Sprinklerforum
Sent: Monday, August 3, 2020 10:48 PM
To: [email protected]
Cc: Sprinkler Academy - C Bilbo <[email protected]>
Subject: Re: sprinklers above mechanical platforms

*** SCDLLR NOTICE ***
  *   This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
  *   Personally Identifiable Information (PII) should not be included in 
e-mail text or attachments. Do not save or transmit PII unencrypted.


The answer to your question depends on whether the wood is fire retardant 
treated or coated.  Treated (as in pressure treated) wood qualifies for the 
omission.  Coated does not.

It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.sprinkleracademy.com&c=E,1,1Ngkc9a68SR_QfINdSutx0vzA1PDWlooW8Eblq2ZxH_w5lVQP72dO7K_Act9lmAWdvYluaDaG_pjOSaCPPYRDmrGGOZjDUS4agb4522-vYdkhV7sDKmo2WK7HYs,&typo=1<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.sprinkleracademy.com&c=E,1,Yn1mz2BYopT7UH3gnrHwbtLa5dvxw-w48KH4R8hMCQrsh_jdglDJ6elR4Fl1uBjtHolqOYWBBho5JJ7K8ns8I7p7WL66UvWSw5mMKn_CRRBxwlN1FAFvdxcJgw,,&typo=1>
[email protected]<mailto:[email protected]>
??
OUR STUDENTS SAVE LIVES!!


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Trillium Fire Sprinkler Design Inc. via Sprinklerforum 
<[email protected]>
Sent: Monday, August 3, 2020 7:40 PM
To: [email protected] 
<[email protected]>
Cc: Trillium Fire Sprinkler Design Inc. <[email protected]>
Subject: sprinklers above mechanical platforms

Can someone please direct me? I have a metal building with acoustical ceiling 
tiles. Above the ceiling they have framed with metal studs and fire rated 
plywood a mezzanine for the AHU's to sit on. These are electric and not gas 
fired.



For some reason I recall reading that if the AHU's are not gas fired then no 
sprinkler protection is required above the area of the mezzanine.



Can someone please clarify?



Regards



Troy

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,dAUuXXBA7G4J-1yyFL8_S2yX1AUSrJFc4qBkepBbyjME_71KKV96eJ0PFC_QGtoPC5cwVOMNxBr3VLdA1H3G1avMpM6NhMiNBXijviU71uC4l2UdBy6OP9g,&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,CLNCY-DrTJjtjWESR1LYvYxApdi1S-BU6gweYj93ZVuNtoipDAfNY3ZA-GBuzClDT9tEarKt4UYluyhlkXnW-aJ9YWzDdJrMcBAZ62t6Mz4jQgjTxpU7&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to