Considering how much corrosion I've observed and documented in wet and dry 
systems in schedule 10 in 8-15 years - not MIC - we only specify schedule 40.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Wednesday, January 20, 2021 11:07 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton <st...@protectiondesign.com>; Matt Grise <m...@afpsprink.com>
Subject: RE: schedule 7 pipe?

Considering how much "Sch. 7" we've seen perforated by MIC, and also that our 
firm is heavily invested in the institutional and educations sectors where 
clients want 50+ year buildings, we only spec' Sch. 10 and 40.   

Steve L. 

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise via Sprinklerforum
Sent: Wednesday, January 20, 2021 7:58 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise <m...@afpsprink.com>
Subject: schedule 7 pipe?

Has there been any push/interest in allowing unlisted (standard ASTM A53) 
schedule 7 steel pipe to be allowed by code in place of the listed "flow" 
piping options?

Matt

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to